gp66

hi all . bit stuck on this one ! instald new 10mm water bond today from cu to water stop tap as no bond was present.the main water into the property is lead as far as the brass stop tap and from the stop tap to the rest of the kitchen is 15mm speedfit plastic ! no copper in site but at the boiler in the next door room it is copper .so wher do i clamp my 10mm earth to ? thanks
 
Hi Mate ! The Lead pipe and the brass stop tap are likely to be both extraneous conductive parts ,therefore you will need to Main bond with a clamp to the pipe [ Trouble here is that BS 951 clamps are not suitable for soft metal such as lead...so you need to sort something else out for the type of clamp ...google it and you will find suitable methods ].

..As for the copper pipework at the boiler ,probably no need to main bond unless it goes into the ground ,and therefore possibly becoming an extraneous conductive part....test back to the met with a wander lead for verification.[ Note : always consult boiler manufacturers data as to bonding requirements ,as they take precedence over the regs.

regards..Sparkylad.
 
the copper on boiler and rads possibly only for show and changes to speedfit stuff under worktop/floor? as for the lead there are clamps avaiable dont be tempted to use normal clips as these could crush lead and cause leak
 
just another bit of info on the subject ..taken from the ESC essential guide....refers to the clamps on Armour or mettallic sheaths


. Misuse of BS 951 clamps
Cases of misuse of BS 951 clamps are occasionally found, some examples of which are given below.
5.1 Fitting a BS 951 clamp to the armour or metallic sheath of a cable
BS 951 states that clamps to this standard are not intended for connection to the armour or sheath of a cable and requires the packaging of the clamp to include the warning “Not intended for use on the sheath or armour of a cable”. This is because the action of tightening the clamp is liable to damage the cable, for example by crushing the bedding or insulation or by causing the metal in a lead sheath to cold-flow. Such damage may result in high resistance and unreliability in the electrical connection between the clamp and the armouring or metallic sheath, and may even result in an electrical fault within the cable, with the possibility of serious injury to persons. Fitting a BS 951 clamp to the armour or metallic sheath of a cable is therefore unacceptable.


regards..---sparkylad
 
i was working in a yard and the spark there thought electrical bonding was sparks going for a few beers.he also asked wot cable to to us for downlighters there was 1.5mm drum of artic cable yellow i said u can use that he told me i was winding him up thats for 110v.
 
i was working in a yard and the spark there thought electrical bonding was sparks going for a few beers.he also asked wot cable to to us for downlighters there was 1.5mm drum of artic cable yellow i said u can use that he told me i was winding him up thats for 110v.


one seems to suggest that the spark was of a sheltered nature and does not think out of the box very often....!! monkey see monkey do!!

what a muppet!!!
 

Reply to Where to bond in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
190
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

M
  • Article
Intermittent bad smell Hi I have an intermittent bad smell that's really hard to pin down, I was wondering if I could get your thoughts on it...
Replies
0
Views
277
MatthewG
M
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top