does anyone know where in the bs:7671, you can find the protective device operating current (I2) ? Ive been looking for quite some time now, and i'm getting rather fustrated, because I cant find it?
cheers luke
cheers luke
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss where to find the protective device operating current (I2) in 7671??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Luke,
we are going deep on this one, its difficult because i dont know the full circuimsatances (and context) of the question
I will try and expand on what i have already said
Your calculations are a bit off
"the current (I2) causing effective operation of the protective device devices does not exceed 1.45 times the lowest of the current-carrying capacities (Iz) of any of the conductors of the circuit"
My interpretation: if you were using singles (for example) and worked out your Iz such that you needed 1.5mm conductors, and you happened to have 2.5mm phase and 1.5mm neutral, then your calcs would be based on the 1.5mm as the "lowest of the current carrying capacities"
Lets say lighting circuit. Ib = 3A (for example)
MCB = 6A so In greater then/ equal to Ib.
Iz for tw/e method 1 =16A
So Ib In Iz is satisfied
Now look at the statement
"the current (I2) causing effective operation of the protective device devices does not exceed 1.45 times the lowest of the current-carrying capacities (Iz) of any of the conductors of the circuit"
So 1.45 x Iz = 1.45 x 16 = 23.2A
So the current causing operation of the MCB should not exceed 23.2A
Type B 60898 has instanteneuos trip current of 3 to 5 x In = 3 to 5 x 6A = 18 - 30A
18 is less than 23.2 so its ok.
But it doesnt matter because :
433-02-01
(ii) its nominal current or current setting (In) does not exceed the lowest of the current carrying capacities (Iz) of any conductors of the circuit, and
(iii) the current (I2) causing effective operation of the protective device devices does not exceed 1.45 times the lowest of the current-carrying capacities (Iz) of any of the conductors of the circuit"
and 433-02-02 says
"where the device is a fuse.....60898......etc compliance with (ii) also results in compliance with condition (iii)
So basically dude they have worked it out for you! This is why this is a grey area which people tend not to refer to: if you have followed Ib In Iz and you are using a standard protective device then I2 (and so 433-02-01 (iii)) doesnt really ever come into it!
You are either now happy
or in a worse state of confusion than when you started
and my typing hand is hurting
have fun!!!
Luke, you can look at this a few diferent ways. As Alan said, you can look at the graphs in the regs, or if you want the instanteneous trip current for cicrcuit breaker type, go to table 7.2b, page 51B
it depends how you phrase the question:-
If you said, how much current does it take for a 32A Type B BS 60898 circuit breaker to operate in a given time (say 0.4S), then you would be on page 199 in the regs. (or how long will it take to operate with a set/calculated/given fault current)
Wheras if you wanted to know the 'trip current' for the same MCB, you would be in table 7.2B This would tell you that a type b has an instantaneous trip current of 3 to 5 times In, so it would take 90-150A to trip the MCB
so i suppose it depends if you are foccussing on time are actual current levels.
To be technically correct, a DEVICE does not have an I2, a CIRCUIT has an I2
I2 is the 'current causing effective operation of the protective device', therefore the I2 value will be dependent on the circuit charecteristics (Zs etc), this will be co-ordinated with the In of the protective device but the two are not the same.
Have a look at 433-02-01 which may help! (or not!)
regards
Tony