Another question please.... quite a few tonight?

Completing EIC certificate, domestic mains board is fed off submain supplied via switched fuse.

Just checking that I take my Ze at switched fuse ?

Thanks,

Sy
 
As Wirepuller , When you do the test make sure you test it with out the bonding to the services connected or you may get false readings
 
Last edited by a moderator:
Again agree with Wirepuller. Youre right Sy , Disconnect Main Earth from the rest of the instation and
Test.That is your Ze.
The Test @ the C/U is the Zs of the Submain.
 
Isolate installation before disconnecting earthing conductor/bonding and reconnect earthing conductor/bonding before re-energising installation.
 
When testing Ze at a DB fed via sub-main, given that bonding conductors and final circuit cpc's are isolated from the test earth in order to avoid parallel paths affecting readings, should any other earths connected at origin of supply such as other sub-main circuits, bonding conductors, etc also be disconnected, leaving only a test to the main earthing point?
 
When testing Ze at a DB fed via sub-main, given that bonding conductors and final circuit cpc's are isolated from the test earth in order to avoid parallel paths affecting readings, should any other earths connected at origin of supply such as other sub-main circuits, bonding conductors, etc also be disconnected, leaving only a test to the main earthing point?

Not sure I follow.

Ze is external to the installation.
 
if its a sub main fed from another dist board it would be Zs and tested like another circuit , the Ze reading will be taken at the first point of the installation after the meters ,isolate the supply remove main earth and test between the L and N and the main earth block
 
remove main earth and test between the L and N and the main earth block

Ze is between the incoming line conductor and the earthing conductor. Parallel paths removed by disconnecting main bonding or disconnecting the earthing conductor (usually easier).

The installation is isolated during this test.
 

Reply to Where to read Ze..? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
312

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top