K

KEVINDOE

Hi all,

Just a quick one on a rod position, I have run a 25mm s.w.a sub-main to a holiday cottage 20 meters from an existing property that has a 3 phase supply. customer has ordered d.n.o to connect the holiday cott to one of these phases. the existing 3 phase supply is T.T.,, now , if availible, i would hope they would connect as p.m.e, but if not at wich end would you recommend the rod for the holiday cott, the supply end or the cott end ??

Thanks:)
 
Last edited by a moderator:
I could tell you where to stick your rod, but I might get banned....

Sorry, couldn't resist. Sorry for being no help.
 
If its done as PME then switchfuse will be fine.
You will also have to make sure that your cpc to the cottage is large enough to satisfy the requirements for your main protective bonding or you will have to make the cottage a TT anyway.
 
Yep, understood, its 25mm swa 3 core, am i right in saying that min would be 10mm to export p.m.e to match min size of bonding conductors??
 
For a PME system the csa of the main bonding conductors must not be less than that given in Table 54.8 ie a 10mm protective bonding conductor for a neutral conductor of 35mm or less. 544.1.1
So check the size of the supply neutral.
 
Yes , agree, but regarding the sub-main, if the bonding conductors are 10mm csa, the the cpc of the sub-main should be at least the same?
 
The 25mm cpc would be fine, however, in this instance i would install a rod, and divorce the cottage from the main house cpc regardless.
 

Reply to where to stick a rod ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
334
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
455

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top