pencilpusher

I have changed the consumer unit in a kitchen. All done. I need to run new swa out to the detached garage to replace the swa thats already there. I am doing this so that I can avoid RCD protection at the house cu. Swa will be run inside and terminted in a box before running T&E to CU. My question is; what certificate do i use re the new swa to garage? I will not be touching any circuits in the garage. Thanks
 
Last edited by a moderator:
If you are changing the SWA which means either a larger or smaller size of CSA and length difference, then you really should fill out an EIC, as you will have affected the Zs values of all the circuits in the garage.

Why not install the swa directly into the CU?

By using the T&E to connect into the garage CU, remember the earth CSA will be reduced.
 
Thanks Mark. The only reason for terminating in a box and then running to CU was because of the lack of room in the kitchen cupboard where the CU is. The swa at the moment runs with T&E through the kitchen wall to an adaptable box on the outside wall where it joins swa. To avoid having to RCD the swa (because garage CU is TT and house is TNCS) and discrimination issues I am changing swa to run inside the house.
 

Reply to Which certificate? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
829
Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
288

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top