We have recently had some work done by contractors at our building.
Double socket in an office, fed in 2.5 FP200, on a 32a MCB.
First question is I wanted to look at the current carrying capacity for FP200 but wasn't 100% which table it is. Is it classed as mineral? Making it 4G1A
Is there anything wrong with the single double socket being protected by a 32a MCB? I personally would have put it on a 20a. But providing the current carrying capacity is more than 26a (the max the 2 sockets can pull) it wouldn't pull more than the cable can take. Hence wanting to find the table first.
And secondly can someone confirm that this should also be RCD protected. Although it's been put in for a specific reason ie a tv, it's still a double socket and could be used for anything else. The cable is not mechanically protected.
I know regulation 411.3.3 says that an exception to the fact a socket exceeding 20a requires RCD protect can be that it is used under the supervision of skilled or instructed persons, would that mean a maintenance electric on site, even though someone could use this socket any when without the maintenance guy knowing?
Hope that makes sense!
We have recently had some work done by contractors at our building.
Double socket in an office, fed in 2.5 FP200, on a 32a MCB.
First question is I wanted to look at the current carrying capacity for FP200 but wasn't 100% which table it is. Is it classed as mineral? Making it 4G1A
Is there anything wrong with the single double socket being protected by a 32a MCB? I personally would have put it on a 20a. But providing the current carrying capacity is more than 26a (the max the 2 sockets can pull) it wouldn't pull more than the cable can take. Hence wanting to find the table first.
And secondly can someone confirm that this should also be RCD protected. Although it's been put in for a specific reason ie a tv, it's still a double socket and could be used for anything else. The cable is not mechanically protected.
I know regulation 411.3.3 says that an exception to the fact a socket exceeding 20a requires RCD protect can be that it is used under the supervision of skilled or instructed persons, would that mean a maintenance electric on site, even though someone could use this socket any when without the maintenance guy knowing?
Hope that makes sense!