I am changing a shower over this weekend and just trying to workout what test i need to do.
I have worked out that I need to do the following
Earth Continuity from cu to shower switch then to shower
500v Insulation resistance test bypassing the neon in the shower switch
L to N
L to E
N to E
Polarity
Is it also worth doing a rcd test.
Have i missed anything
 
You need to do the R1 & R2 test followed by an IR test L to CPC N to CPC joint the L and N together and test between the cpc you need to do it this way as youll have neons in circuit plus the shower which will give incorrect readings ,be carefull doing this at 500 volts if its a micro processor controlled shower , then you need to do the Zs and RCD tests ,RCD ,push the button x1 and x 5 the polarity will be confirmed twice once when doing the R1 & R2 and again when doing the Zs
 
Last edited by a moderator:
Don't forget to do your Zs Tests. Is the shower a like for like change as if its a higher W shower then you will need to make sure that the cables and protective devices are correctly selected.
 
should be fine. final test to be done is test for hot water, should come out of that funny looking rose on a snake.LOL.
 
I am changing a shower over this weekend and just trying to workout what test i need to do.
I have worked out that I need to do the following
Earth Continuity from cu to shower switch then to shower
500v Insulation resistance test bypassing the neon in the shower switch
L to N
L to E
N to E
Polarity
Is it also worth doing a rcd test.
Have i missed anything

If you not altering the existing cable or protection device then you really don't have to do any testing as such. If your going to issue a MEIWC then you will have to do all the tests highlighted on them.

IMO I would always issue a MEIWC so therefore do all the tests, if your not use to testing it's a great way to practice.
 
I aways test even if im not altering the wiring as it the only way i can be sure that the wiring is correct and safe you could have a broken earth or loose connections in the switch so checking and testing is the way to confirm this
 
First things first you have satisfy your self that that the KW of the shower and the cable have been corrctly matched so many times a customer has phoned me to ask can I change a shower only to find its a 10KW and the cable is 6mm
Pict
 

Reply to Which test to carry out on a shower install in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top