Hi,

When changing a board for someone, what method do you use to obtain R1 + R2?

When I do it, I cross connect at the CU and measure at each point, and on a radial link between and measure at each point.

Does anyone just calculate it on a ring by doing this:

(r1 + r2) /4 = R1 + R2

Just seems to take me a ages doing a board change and wondered if I'm missing a trick here?
 
yes, (r1+r2)/4 = an expected value of R1 + R2 at sockets. I do that calc, then at the end when doing my Zs readings do Zs-Ze to get a calculated R1+R2 and it should be thereabouts (unless spurs). A lot of DB change EIC's I see have nothing in the R1+R2 box!
 
Like I said I do the three step process and cross connect etc to check for polarity etc, just wondered who calculates it on a board change opposed to going round each and every point measuring it?
 
yes, (r1+r2)/4 = an expected value of R1 + R2 at sockets. I do that calc, then at the end when doing my Zs readings do Zs-Ze to get a calculated R1+R2 and it should be thereabouts (unless spurs). A lot of DB change EIC's I see have nothing in the R1+R2 box!

Thats bad leaving boxes empty! Zs-ze shouldn't be relied upon due to parralel paths etc, but I guess it will give you a rough idea. Presumably then you don't go round each socket or light fitting then?
 
I don't cross connect on a db swap. Like I stated I take Zs reading, then Zs-Ze that is my R1+R2.

- - - Updated - - -

I take Zs at every point.
 
Im not doing initial verification of all the circuits, Im changing a consumer unit. I just interested in correct OC protection, satisfactory insulation resistance and satisfactory disconnection times.
 
Very true, I suppose it's just something I have always done to satisfy what I'm doing being relatively new to the trade I prefere to be thorough, maybe time for a change, I'll get things done quicker then.

I picked up another rewire today which was good, 4 bed house, 1930's, nice job, the bloke works for WPD so I'll get him to stick an isolator in and a new shiny service head etc, I'm sure he can wangle that for free.
 
Very true, I suppose it's just something I have always done to satisfy what I'm doing being relatively new to the trade I prefere to be thorough, maybe time for a change, I'll get things done quicker then.

I picked up another rewire today which was good, 4 bed house, 1930's, nice job, the bloke works for WPD so I'll get him to stick an isolator in and a new shiny service head etc, I'm sure he can wangle that for free.

Nice one, Obviously go the whole hog on testing that install being a new job an all.
 

Reply to Which way do you do it?H in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
340
You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top