Hi,
Had a look at a job today and noticed external lighting had been wired in white FP, clipped to wall surface.
I informed them mechanical protection must be provided and they insisted the board had RCD protection and it wasn't required.
Anyone else seen this before.
mechanical protection would only be required if there was a danger of the cable suffering impact damage. what's also relevant is that FP will degrade due to sunlight etc.
Was working on the roof of a huge department store a few years ago and miles of white fp was on trays to the ac units, most of the sheath was dust on the floor.
Interesting. According to the manufacturer, FP200 can be used externally. From the manufacturer's data sheet:
Sheath
Robust thermoplastic low smoke, zero halogen and reduced flame propagation outer sheath. Standard colours white and red with bespoke colours available to special order. Suitable for outdoor installation with exposure to normal daylight UV.
http://www.fpcables.co.uk/FP200_Gold_Prysmian_2.pdf
So, as per Telectrix's first sentence, mechanical protection only required if likelihood of impact damage (or some other external influence).
Is it confirmed Prysmian FP200? Or perhaps some other "equivalent"?
Sheath
Thanks for everyone's replies.
Ive not confirmed what exactly, but I expect it wasn't Prysmain fp200 and more likely a cheaper equivalent going by the quality of light fittings.
Reply to White FP external use in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Red fp200 gold and white FP200 from Pyrsiiam are both UV rated. That said they both eventually show signs of being outside and I used to avoid...
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...