nickblake
Just answered a question on another post ,and it dawned on me , yippee the brain kicked into gear , i have read on loads of posts that people say doing an inspection just calculate the R1R2 by doing a Zs and taking away the Ze , i have never liked this method and heres a reason why , supplimentary bonding !!!!! you go into a house you do an R1R2 test you get a reading if there are any open circuits it shows up and it can be rectified , so what happens if the install is up to 16th edition all supplimentary bonding is in place ,3/4 the way through the lighting circuit there is a bathroom with an electric shower , you find the last on the run bedroom next to the bathroom quick Zs all ok , heres the scinario , the cpc's have have been cut off at the first light switch , metal clad switches and light fittings , so you test the last on the run get a good Zs reading fill in the sheet calculate the R1R2 and walk away ,so what if the supplimentary bonding has been installed between the shower and the light as it was in the 16th edition ,you then will have a reading which is false and potentially leave the entire un earthed circuit thinking its ok , so the moral of the thread is R1R2 Insulation and Zs simples easy to see the supplimentary bonding and and not put 2 and 2 together , thank you malcom for kicking my brain into gear on this one just a comment he made made me think :devilish: