You say you don't understand and then in the next breath say the thermostats have been shorted out.
The manufactures fit the thermostats instead of timers for a reason. You will also find they are set lower than the maximum temperature, this is to take in to account the thermal build up during a subsequent start. The thermostat should be wired in the start PB circuit so it can’t stop the drive during start up, only prevent it starting. Most will have a manual reset over temperature thermostat set above the maximum temperature to sense a locked rotor, this will stop the drive.
Does the idiot that shorted out the thermostat still have a job?
You obviously don’t know how these drives work. It would be far better if you left well alone.
The manufactures fit the thermostats instead of timers for a reason. You will also find they are set lower than the maximum temperature, this is to take in to account the thermal build up during a subsequent start. The thermostat should be wired in the start PB circuit so it can’t stop the drive during start up, only prevent it starting. Most will have a manual reset over temperature thermostat set above the maximum temperature to sense a locked rotor, this will stop the drive.
Does the idiot that shorted out the thermostat still have a job?
You obviously don’t know how these drives work. It would be far better if you left well alone.