Round 2 with EDF. Different meter man turns up today to connect my new supply. Has the usual walk round site checking my bonding etc all OK. Checks my new switch fuse, meter tails etc all OK. Askes what size my sub main cable is to which I reply, 25mm 4 core swa. Askes if I am using the armouring as my main cpc to which I reply yes. Looks at me and says well I cannot connect as the armouring is of insufficient size as I must have a minimum csa of 16mm. I then try to explain to him that the csa of the armouring was calculated and worked out to be more than sufficient for this new supply. He then phones his boss and comes back to me and says not allowed to connect. Asked him if he could give me 5 minutes to prove he was wrong and with that he handed me a failure notice, got in his van and drove off!!!
I have double checked this again using in section 543 using tables 54.4, 54.7 and 43.1 and basically the armour equates to a csa of 70mm in steel which is the equivalent csa of 22.5mm of a copper cpc. A completely wasted day, most of which was spent on the phone trying to get through to someone sensible at EDF.
I have double checked this again using in section 543 using tables 54.4, 54.7 and 43.1 and basically the armour equates to a csa of 70mm in steel which is the equivalent csa of 22.5mm of a copper cpc. A completely wasted day, most of which was spent on the phone trying to get through to someone sensible at EDF.