Because in effect the tails become a submain & as such will require a cpc + ocpd suitably rated for the load length of submain & csa of cable.
I think you may be trying to look into it too deeply.ok, thanks for that Jason. I'll accept that that's the way it is, though if the tails are the customer's, then why are the DNO involved? If the DNO's supply cable went 15m further, do they make any adjustments to the fuse fitted?
As you can see, I've not quite got itSorry.
I think you may be trying to look into it too deeply.![]()
more length is better
though if the tails are the customer's, then why are the DNO involved?
Because it is THEIR equipment that the tails are connected to.
but are they?
the tails are connected to the meter, and that is not the DNO's, that is your electricity suppliers, your DNO's property ends at the incoming fuse![]()
my mrs says that i need to increase my cross sectional area!!!
Thats correct, however, the DNO own the supplying cable, fuse etc (the important bit). the meter is only to monitor usage, not to provide any fault protection.
Therefore, they have the final say on how you connect your installation to THEIR supply.
Some DNO's will not connect a new supply without seeing an install certificate from an NICEIC or ECA registered member.
You are thinking far too much about this!!!