LearnerDave

Hello,

I wonder if anybody could point me in the right direction to find out why 0.1s is used as the time in the adiabatic equation with regard to the main earthing conductor?

I can find the table 41.1 for final circuits not exceeding 32A, and 411.3.2.3 - TN = 5s and 411.3.2.4 - TT = 1s, but I am struggling to find any reference to the 0.1s!

Any pointers would be much appreciated.

Cheers Dave
 
look at the time/current curves in brb. say for example you have a 80A BS1361 fuse and your pefc is 1100A. p244 will show that that fuse will break in 0.1 sec. with that fault current. say your fault current was 800A, then the value for t would be 0.4sec.
 
Last edited:
Thank you very much Telectrix. The penny's dropped - You use the on site measured PEFC to determine the time the protection device will discconect in, and also use it for I2 of the adiabatic equation. Phew, thats been bugging me for days.

Thanks again. Dave
 

Reply to Why 0.1s for Main Earthing? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
137
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
928
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
792
loz2754
L
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
495

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top