Why are there 2 inputs on my inverter when i only have 1 mppt, the installers have doubled up (in parallel) the 2 strings in the dc isolator and wired 1 set of leads from that to 1 input, should they have used both inputs ??
thanks for replys its a 3.64kw system with 2 strings of 7 panels, just wondering why itsnot wired to the two inputs on the inverter as i have 4 wires going to roof an 2 out of dc isolator should there not be 4 ?
Depending on the make and model of inverter some are commoned inputs 1 & 2. Meaning even if each input was used the overall connection would be the same as a single connection.
I don't know what inverter you have but the figures look ok. They will have needed to wire the system like that so that your voltage doesn't exceed the maximum of the inverter.
I think it is good practice to have a DC isolator for each string though.
I think madmaz's query relates to why both strings are plumbed into one isolator then into one input of the inverter, rather than into 2 isolators and into both inputs of the inverter. I'd say it was down to penny pinching or laziness. Nothing intrinsically wrong with doing it this way, providing the isolator and outgoing cable is sufficiently rated (most likely is) but I would prefer to see each string into its own isolator.