tony.towa
Was sent today to a large branch of a major retail chain where they had reported their outside lights at the loading bay were not working.
Got there to find to 70watt Mini SON fittings (with built in photo-cells) as they said, not working.
Looking at the building from the back the first fitting is on the right hand wall. Opening up the fitting there was no voltage at the connector block. Off to the switchroom to check the breaker. Nothing marked up on the board for outside lights and all the breakers on. Time to wander round the store to find the other dbs fed from the board. First one found, labelled Distribution board E - all breaker on and nothing for outside lights. Off on my wandering again - found db D same result as E. Wander again and ask a few questions dbs A B and C do not exist. Time to trace the cable.
Flex from fitting goes into conduit and down to an end box, choc block in there connecting to 1.5 T&E. Into the store, lift ceiling tile and find the cable. To cut a long story shot (thank goodness I hear you cry) source of cable eventually found on left hand wall, above ceiling, an unswitched FSU tapped of a final ring circuit. The fuse was blown. Replaced it changed the lamp, covered the sensor and the light came on.
Logic says the other fitting should be linked with this one. Why are things never logical. Changed lamp, no go. Got reflector out and saw the tell tail brown marks on the ballast.
Got a replacement fitting and pulled the fuse in the spur unit. Still 240volts at connector block in lamp. Followed conduit through store to switchroom and it terminated at the emergency lights test switch.
Switched the switch to test and no voltage at fitting (note to self must remember to tell manager next time I do this as 25% of shop floor lighting went off)
Changed the fitting and traced the feed to a maintaind unit over one of the storeroom exit doors.
We are not allowed to do "major work" without prior authorisation so took the feed from the fitting and extended it back to the original spur (as a temporay measure) to await authorisation to run a new circuit from one of the dbs.
Why the heck do people, who are "professional electricians" install things in this manner, especially when you consider the company concerned is a member of the NICEIC!!!!!
Got there to find to 70watt Mini SON fittings (with built in photo-cells) as they said, not working.
Looking at the building from the back the first fitting is on the right hand wall. Opening up the fitting there was no voltage at the connector block. Off to the switchroom to check the breaker. Nothing marked up on the board for outside lights and all the breakers on. Time to wander round the store to find the other dbs fed from the board. First one found, labelled Distribution board E - all breaker on and nothing for outside lights. Off on my wandering again - found db D same result as E. Wander again and ask a few questions dbs A B and C do not exist. Time to trace the cable.
Flex from fitting goes into conduit and down to an end box, choc block in there connecting to 1.5 T&E. Into the store, lift ceiling tile and find the cable. To cut a long story shot (thank goodness I hear you cry) source of cable eventually found on left hand wall, above ceiling, an unswitched FSU tapped of a final ring circuit. The fuse was blown. Replaced it changed the lamp, covered the sensor and the light came on.
Logic says the other fitting should be linked with this one. Why are things never logical. Changed lamp, no go. Got reflector out and saw the tell tail brown marks on the ballast.
Got a replacement fitting and pulled the fuse in the spur unit. Still 240volts at connector block in lamp. Followed conduit through store to switchroom and it terminated at the emergency lights test switch.
Switched the switch to test and no voltage at fitting (note to self must remember to tell manager next time I do this as 25% of shop floor lighting went off)
Changed the fitting and traced the feed to a maintaind unit over one of the storeroom exit doors.
We are not allowed to do "major work" without prior authorisation so took the feed from the fitting and extended it back to the original spur (as a temporay measure) to await authorisation to run a new circuit from one of the dbs.
Why the heck do people, who are "professional electricians" install things in this manner, especially when you consider the company concerned is a member of the NICEIC!!!!!