hi ,
Input primary 2 phase 415V with SCR control .
its was trips after trigger SCR .
if direct connection primary 415V without SCR , no trips happen .
I was wondering root cause of over current 100A MCCB keep on trip ?
Seeking advice

regards
 
hi ,
Input primary 2 phase 415V with SCR control .
its was trips after trigger SCR .
if direct connection primary 415V without SCR , no trips happen .
I was wondering root cause of over current 100A MCCB keep on trip ?
Seeking advice

regards
You mention that when the SCR is out of circuit no trip occurs, whilst working on AGL installations, we found that O\on start up the SCR drew an inordinate amount of Amps when compared to normal run Amps, could this be a inrush problem? maybe the wrong type of OCPD is being used, just throwing this around, for comments, but the OCPD was changed and it cured the problem, please don't ask me what sort or size it was when I was a lot younger than I am now, hope this throws some light on the subject, fingers crossed.
 
Yes it may be a result of where in the mains cycle the SCR fires. When continuously energised, the transformer magnetising current (and therefore the flux) lags the voltage by a quarter-cycle. If the SCR fires at or near the supply voltage zero, the flux is also at zero when it would normally be at peak value, i.e the phase angle between them is wrong. The following voltage half-cycle then drives the flux to twice the normal peak value. If this causes the core to saturate, the inductance falls drastically and with it the primary impedance, resulting in a heavy overcurrent that trips the breaker. The same thing would happen when switched on at the voltage zero by chance rather than by the firing circuit, so if it occasionally trips when switched on by hand without the SCR control that is a clue that this is the reason the trip. Also, snubber networks subjected to high dV/dt can pass high instantaneous currents. As Pete says the MCCB is probably unsuitable for this duty.
 

Reply to why does 35KVA Transfomer for spot welding tripping? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Have you tried them without the PIR in the circuit? Could be a dodgy relay in the PIR. LEDs are not technically always on but pulse really fast so...
Replies
1
Views
357
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top