Went to a house this morning to locate a fault causing the RCD in a split load board to trip.
Going through the usual tests, I decided to put my earth leakage clamp meter on the earthing conductor.
Here is where it gets weird: with the main switch in the off position, the meter was reading nearly 3 amps through the earthing conductor!!!
So I decided for a giggle to put the clamp around a nearby gas pipe, and got around 1.7 amps through the gas pipe!!!
Ze was 0.30 ohms on what appears to be a TNC-S. Polarity is fine.
Can anyone explain this please?

[ElectriciansForums.net] Why does my current clamp meter show large current in gas pipe?
 
Think more outside the box (assuming the clamp meter is correctly calibrated and not low on battery) fault currents may not be from within the property but using the local gas mains as a route to the good earthing of the property, there may be a fault locally in ground around the property, this may have no relationship to the property electrics at all but regardless this can be very dangerous situation especially to other tradespeople like plumbers who may alter the pipe work and expose themselves to deadly currents.
 
this can be very dangerous situation especially to other tradespeople like plumbers who may alter the pipe work and expose themselves to deadly currents.

we can only hope. ?. maybe there is a God after all.
 
Incidentally, in case anyone was wondering, I traced the RCD tripping fault to a dodgy cable in the upstairs sockets circuit. Nothing to do with my question about the current flow in the had pipe.
so did you check the current in the gas pipe/MEC after fixing the fault?
 
Think more outside the box (assuming the clamp meter is correctly calibrated and not low on battery) fault currents may not be from within the property but using the local gas mains as a route to the good earthing of the property, there may be a fault locally in ground around the property, this may have no relationship to the property electrics at all but regardless this can be very dangerous situation especially to other tradespeople like plumbers who may alter the pipe work and expose themselves to deadly currents.
Yes this what I concluded.
I disconnected the main earth and tested for voltage between the main earth and neutral- 0 volts. Tested between gas pipe and neutral- 0 volts.

Not sure what I should to go about making this safe...
 
Assuming both Main protective Bonding connections are in place, and your confirmation that Ze is good, I cant see there is a lot you can do.
Its always possible its originating from a neighbouring property with a fault maybe?
I watch this thread with interest.
 
Assuming both Main protective Bonding connections are in place, and your confirmation that Ze is good, I cant see there is a lot you can do.
Its always possible its originating from a neighbouring property with a fault maybe?
I watch this thread with interest.
I'm guessing it originates outside this property, as the current was there with the main switch off.
Maybe I should recommend the customer gets in touch with the DNO.
 
I read about this somewhere before. IIRC it's to do with it being TNC-S.

Your neutral back to the transformer is shared with your neighbour. Your neutral is also connected to the gas pipe via bonding. Your gas pipe is shared with your neighbour, who also has it connected to neutral via bonding. So you have in effect 2 conductors in parallel, the neutral, and the loop bypassing part of the neutral via bonding + gas pipe.

Some current making its way home will flow through the gas pipe + bonding. That's kinda what i read, anyway
 
Wonder what potential difference you would get between the two sections once disconnected?
I don't know. I measured the disconnected ends of the bonding and earth cables to neutral, but of course the neutral is connected to the supply main earth, so without a reference earth, I got 0 volts.
 

Reply to Why does my current clamp meter show large current in gas pipe? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top