Why does RCD trip when measuring voltage with LoZ function? | on ElectriciansForums

Discuss Why does RCD trip when measuring voltage with LoZ function? in the UK Electrical Forum area at ElectriciansForums.net

Presumably you are testing from live to earth here?

As it is a low impedance test it will be allowing enough current to flow through the tester to exceed the tripping threshold of the RCD.

Does it always cause an RCD to trip or has it happened with one specific RCD or installation?
 
Presumably you are testing from live to earth here?

As it is a low impedance test it will be allowing enough current to flow through the tester to exceed the tripping threshold of the RCD.

Does it always cause an RCD to trip or has it happened with one specific RCD or installation?
Hi Dave, thanks for answering, it happened twice so far with rcbo's in different houses when measuring voltage between active and neutral with the low impedance function.
Probably just very sensitive rcbo's, I was wondering if someone else experienced the same and see if there's a guess why.
Cheers!
 
Hi Dave, thanks for answering, it happened twice so far with rcbo's in different houses when measuring voltage between active and neutral with the low impedance function.
Probably just very sensitive rcbo's, I was wondering if someone else experienced the same and see if there's a guess why.
Cheers!

Why were you using the low impedance function to measure the voltage rather than a normal, high impedance, voltage measurement?

It may not be that the RCBO's are over-sensitive, it's more likely that there is already some leakage on those circuits and the additional current takes it over the tripping threshold.
 
Why were you using the low impedance function to measure the voltage rather than a normal, high impedance, voltage measurement?

It may not be that the RCBO's are over-sensitive, it's more likely that there is already some leakage on those circuits and the additional current takes it over the tripping threshold.
I was fault finding and at some stage used LoZ function to check ghost voltage, I looked for leakage with leakage clamp but there was none, I probably should have done a ramp test to check the sensitivity of the rcbo.
 
I'm assuming that you're using a multi meter such as Kline or fluke with a loZ function to do the measurement ?.

L to N should have been fine, L to E or N to E would probably cause the rcd to trip.
 

Reply to Why does RCD trip when measuring voltage with LoZ function? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Is this a rcbo consumer unit ?
Replies
2
Views
204
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
295

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top