just watched niceic testing dvd tony cable says you can get your ze by enquiry to the local dno but why the way i was shown while ago was to test at your db with main switch off and in coming earth disconected and the test with my 3 probe tester hence im getting 0.02 why cant that be my ze dont need to phone anyone your thoughts please
 
in certain cases, mostly industrial, you can't turn the installation of ( because things are running ) and so can't disconnect the earthing conductor to do your Ze testing. that's when you have to obtain it by guesswork (sorry, enquiry)
 
bs7671 states you can get your ze by enquirey or direct measurement. In some cases you cant isolate the installation so you cant get a proper reading with the earth conected, so sometimes enquirey is the only option.


Jay
 
Because it is not always possible to Isolate the installation, think factories etc., even some domestic installations it is not possible, blocks of flats etc.
 
just another one lads eicr sheets top of page 5 of 9 it asks for zs but said to be completed only if the distribution board is not connected directly to the origon of the installation i gather they mean a sub board were it wouldnt be ze but it would be zs is that right thanks in advance
 
just another one lads eicr sheets top of page 5 of 9 it asks for zs but said to be completed only if the distribution board is not connected directly to the origon of the installation i gather they mean a sub board were it wouldnt be ze but it would be zs is that right thanks in advance

This is normally known as Zdb.
 
in a nutshell, Zdb, is the Zs of the submain supplying the Db. I reckon if i phoned the dno, about the treatment works i work on, most of the time, they wouldnt have a clue about wht the Ze was.
 
I did a rewire a bit ago and when I first went round to have a look at the supply I noticed it only had a 1.5mm main earth, so I told the customer to ring DNO and ask them to upgrade it. Anyaway a few weeks later the DNO came out and upgraded the whole head and moved it into the cellar. When I went back to start the install I had a look at the new head and the engineer had put a sticker on with the type and ampage of the fuse, the pfc and the ze readings. And they did all this for free. I still measured the Ze and pfc and they werent far out.


Jay
 
If you ask the DNO they will probably give you values such as 0.35 or 0.8 Ohms with a pfc of 16.5kA. Which is not what you will want to hear.

Measurement is by far the easiest method, but with larger installations your instrument will probably not be able to give an accurate reading, particularly if it is below 0.2 Ohms (>2kA for 3-ph). You will be dealing with Rline and R1+R2 impedance's of < 0.01 Ohms

You will need to know the Ipsc/pfc(max) for cold working and the Ipsc/pfc (min) operating temperature.

Ipsc(max) = Uo/( Z% +Zline); Ipfc(max) = U/(Z% + Zn or Z2)

Now you can work out the expected fault currents for the actual operating temperature.
 

Reply to why enquire about ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top