hello peeps,

got a quick question i would be most greatful to get an answer to:

Why do the requirements of the 7671 for PFC may not permit the use of a BS3036, semi enclosed device as means of covercurrent protection on a home re-wire

regard magy
 
so im i right in guessing this question is asking why we wouldnt choose bs3036 over newer RCDs?

and basically it because it doesnt have the right min disconnection times

MCBs, not RCDs! it's not just the disconnection time, it's also the low kA rating. MCBs are rated far higher in terms of breaking capacity.
 
why would you even want to use 3036 fuses on a rewire, anyway. that's like using a WWI biplane to combat MIG 29s.
 