hello peeps,

got a quick question i would be most greatful to get an answer to:

Why do the requirements of the 7671 for PFC may not permit the use of a BS3036, semi enclosed device as means of covercurrent protection on a home re-wire

regard magy
 
hello peeps,

got a quick question i would be most greatful to get an answer to:

Why do the requirements of the 7671 for PFC may not permit the use of a BS3036, semi enclosed device as means of covercurrent protection on a home re-wire

regard magy

Because the breaking capacity of a BS 3036 fuse is typically between 1 and 3kA so in situations where measured PFC exceeds this, the device cannot comply.

There is of course back-up protection from upstream devices but the above will answer the exam question.
 
so im i right in guessing this question is asking why we wouldnt choose bs3036 over newer RCDs?

and basically it because it doesnt have the right min disconnection times

MCBs, not RCDs! it's not just the disconnection time, it's also the low kA rating. MCBs are rated far higher in terms of breaking capacity.
 
why would you even want to use 3036 fuses on a rewire, anyway. that's like using a WWI biplane to combat MIG 29s.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
North

Thread Information

Title
why is the use of bs3036 not permited
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
paulthemagpie,
Last reply from
paulthemagpie,
Replies
21
Views
17,882

Advert

Back
Top