alanl
I've had 2 instances in the last week where the Zs measured result was higher than I would have expected.
Firstly, a brand new shower feed, R1+R2 of .11ohms, *Ze (measured) of .31.
I would expect a measured Zs of between .35 and .45 for this, yet it was .55ohms.
Then yesterday, connected a new boiler to an old feed. 2 metres of cable, gave a R1+R2 reading of .05ohms. TN-C-S, I didnt measure Ze, but in a suburban village, so unlikely to be above .35ohms. Anyway, measured Zs was .58ohms.
Clearly both are well within limits, but I cannot see why the measured Zs is higher than a calculated reading, as I would expect the measured one to be lower due to parallel earth paths.
Any thoughts?
Thanks
Alan.