I have just completed an EICR.
The install is TT, Ze is 308 ohms.
Zs on all circuits is <1.5 ohm due to bonding.
There is an up front 30mA RCD which trips with the push button but does not trip when tested either at a socket, light or actually in the RCD itself.
I know the RCD is faulty as I had a spare RCBO which I used and tripped as it should.

The lighting circuit had N-E IR readings of 0.27ohms. All other circuits were >2M ohms.

My question is why did the RCBO not trip instantly when I powered up this circuit through the RCBO?
 
My initial post may sound a bit confusing as I'm tired!

Put simply, the IR test N-E is 0.27 ohms not M ohms and the RCBO does not trip when the circuit is powered up. It trips as it should do when tested.

Why does it not trip instantly when the circuit is energised with a N-E fault of 0.27ohms?
 
My kewteck 64 does not trip an rcd on a TT system if the Ze is too high. If it’s over 300 - 400ohms.

This has happened a couple of times.

If I put an additional rod in lowering the Ze it works fine.

Don’t know why.
Inhibition of excessive touch voltage.
 
The neutral return even though there is a fault to earth which sounds like a solid connection between the two may not necessarily decide to follow the earth path. It just keeps to the neutral because it is possibly the path of least resistance being a TT system hence no imbalance.
 
Your relatively high 270 thousand ohm resistance of neutral to earth (combined with a high resistance earth return) is sufficiently high enough that there is not enough leakage to earth to imbalance the RCBO in the normal working conditions
 
My kewteck 64 does not trip an rcd on a TT system if the Ze is too high. If it’s over 300 - 400ohms.

This has happened a couple of times.

If I put an additional rod in lowering the Ze it works fine.

Don’t know why.
Yes, but the zs is <1.5ohms.
 
Your relatively high 270 thousand ohm resistance of neutral to earth (combined with a high resistance earth return) is sufficiently high enough that there is not enough leakage to earth to imbalance the RCBO in the normal working conditions
It's 0.27 ohms Des, not 0.27M
 
.
There is an up front 30mA RCD which trips with the push button but does not trip when tested either at a socket, light or actually in the RCD itself.
I know the RCD is faulty as I had a spare RCBO which I used and tripped as it should.

When you tested at the RCD did you disconnect the outgoing conductors or disconnect L and N of every circuit?

How does the tripping of your spare RCBO prove that this RCD is faulty? Surely all that proves is that you have a working RCBO?
Testing the RCD with all outgoing conductors disconnected proves whether or not the RCD is working.
 

Reply to Why isnt the RCD tripping? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
350
Ok I’ll try this when I’m down
Replies
4
Views
397

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top