I have just completed an EICR.
The install is TT, Ze is 308 ohms.
Zs on all circuits is <1.5 ohm due to bonding.
There is an up front 30mA RCD which trips with the push button but does not trip when tested either at a socket, light or actually in the RCD itself.
I know the RCD is faulty as I had a spare RCBO which I used and tripped as it should.
The lighting circuit had N-E IR readings of 0.27ohms. All other circuits were >2M ohms.
My question is why did the RCBO not trip instantly when I powered up this circuit through the RCBO?