Why my circuit breaker is tripping. | on ElectriciansForums
Discuss Why my circuit breaker is tripping. in the DIY Electrical Advice area at ElectriciansForums.net
Serg00
Uk
Hi everyone, no sure this question should be in this forum, but im sure a lot of you will know the answer. I've set up a hot box to deliver food in my van. I've put a leisure battery 130ah and a inverter of 1000w continuous 2000w peak. between the battery and the inverter i've put a 100A circuit breaker. The hotbox head output according with the description is 810w, my circuit breaker at times trips, any idea why this is? TIA
Hotbox Rieber thermoport - orange - heated - TP 4.0 1000 KB - https://www.horeca.com/en/product/5487/rieber-thermoport-orange-heated-tp-4-0-1000-kb
Inverter 1000W (2000W Peak) Modified Sine Wave Inverter (Outer Ctn Qty: 5) - https://www.streetwizeaccessories.com/catalogue/product.aspx?node_id=d88a4482-037a-4911-980e-a72e00b9ad15
100A MCB? Is that a typo?!
Instructions for the inverter say it should have a direct connection to battery, it has fuses onboard (3 x 35A)
because the unit can do 2000W peak power, it is possible that for short durations it may be using 160A therefore a circuit breaker if it has a fast trip curve may not be the best thing to protect the cable with, if it were me i think i would use a 180A fuse.
Also note, it says it is not suitable for class 1 appliances. is the hot box class 1 or 2?
Reply to Why my circuit breaker is tripping. in the DIY Electrical Advice area at ElectriciansForums.net