It is not allowed in the US I juust found out when I rehabed the apartment .The wiring was updated about 12 years ago for these 3 rooms so all of the new wiring has a ground other than the line that comes from a junction box and I am going to be running a new line with a ground in a couple days. It was the reversed hot & neutral that I wasn"t sure about. Why is this happening?
How are you testing this apparent polarity reversal?
I don't see how you can test polarity without a ground to use as a third point of reference.
If you measure between hot and neutral you will see 120V (if I understand USA terminology and voltages correctly) if you swap the leads of the tester you will measure exactly the same voltage. AC doesn't have an easily established polarity the same way DC does, it is only when you bring a third point of reference into the measurements, such as a ground, that you can establish a polarity.
Once you have a ground you can measure between hot and ground, then neutral and ground to establish which one is at ground potential and which one is at 120V to ground.
If it is a tester, such as a socket tester, which connects to hot, neutral and ground then gives simple results such as OK, polarity reverse, missing neutral etc then being totally without a ground it will lijely be confused and behave erratically.
[automerge]1593282972[/automerge]
Gasoline all you need to do is take the receptacle out and the black wire goes on the gold screw and the white goes on the silver screw. That’s where your polarity is crossed
We don't know for sure that the polarity is wrong, we only know that there is no ground and an unknown type of tester has indicated a wrong polarity. This could easily be the tester being unable to function correctly without a ground and giving a false reading.