S

s.keech

Hi just been called to a 1960's concrete flat to move a couple of lights and nderfloor heating in the bathroom. The c.u is a metal box with rewirables,very old. The red and black cables are running through metal conduit but there is no earth. Does this mean that the conduit is used as earth. I have looked in the old sockets and they have no c.p.c nor do the lights. I know bathrooms have to be notified to. It also has to be rcd protected to. How would i check continuity,wander lead connected to metal box and check all points or wander lead on m.e.t. There is no earth coming from m.e.t to the metal c.u box though. Is this how they done things before.
Have advised that needs a new c.u but would this need a complete rewire to comply or can i still use the metal conduit as earth.
Any info needed please
Steve
 
if the conduit gives goor R2 readings, as you say, using a wander lead, then use it. the MET will be the earth bar in the CU. are the cables PVC or VIR? if PVC and your IR readings are OK< then they can be left .
 
Oh dear, sounds like a old council flat did some rewires on these years ago. Any adjustments would most likely have to be surface mounted.
 
I did miles of conduit and trunking installs in the late 60's / 70's with using the conduit and trunking as earth.
Very common way of doing it.
 
what you need to bear in mind, when using conduit as cpc, is that you must fit fly leads from back boxes to faceplates, as this is the only way of connecting the cpc to the accessory. ( not required with plastic switches , but necessary on all sockets )
 
what you need to bear in mind, when using conduit as cpc, is that you must fit fly leads from back boxes to faceplates, as this is the only way of connecting the cpc to the accessory. ( not required with plastic switches , but necessary on all sockets )
The bolts are conductors Tel
Yeeeeeeeeeeehhhaaaaaaaahhhhh!!
:)
 
you would fit RCD protection where required. as most cables buried are protected by earthed mettallic conduit, you would only need RCD protection on socket oulets and all batrhroom circuits.
 

Reply to why on earth in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Thanks Brian. I'll keep doing it then, no harm I suppose. I am lucky in that being DIY, I have the luxury of time when it comes to this kind of...
Replies
4
Views
2K
I think I've found the answers to my questions... I can just do a straight forward wiring i.e. connect the 3 wires from the armoured cable to...
Replies
7
Views
829
It's not relevant what NIC expect, they're not an authority. All that matters is regulations and the installers interpretation of them. Either...
Replies
44
Views
4K
There is a section on the mains supply which will give the type of supply as TNS, TNCS, TT etc this indicates the method of earthing
Replies
21
Views
793
The manufacturer has stuck a label on the baseplate, its clear to see. I don't know what instructions came with the fitting or what was written on...
2
Replies
37
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks