Why the need for an earth spike test kit? | on ElectriciansForums

Discuss Why the need for an earth spike test kit? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,292
Reaction score
6,532
Location
Gloucestershire
I am about to put in a copper rod to TT a garage.

I have a megger 1731 but do not have the Earth spike test kit.

I will be able to test the Ze once the rod is in place and wondered what the difference is between testing the Ze and testing the Ra with a spike test kit?

Is it sufficient to just test the Ze rather than purchase a test kit to test the Ra. Will the result be the same? I.e. Ze = Ra

I'm not entirely sure if my terminology is correct, I know Ze is for the external EFLI and am assuming Ra is when you use a test kit rather than the live test?
 
Ra is the sum of resistances of the electrode and earthing conductor and does not include the line resistance as Ze would. Ze is measuring the earth fault loop path, Ra is only measuring the electrode and earthing conductor.
 
Carrying out an EFLI test (test method E3 in GN3 page 64) on a rod is an acceptable method.

I only used spike kits on new installations where there was no supply available and for initial verification.
 
We Ra test all the time.

@happyhippydad I might have a spare Megger Ra test set if you want it. 3 sets of leads and the probes. Just PM me and I'll search it out of the storage box :)
Richy, that's really kind of you :)
I'd love to have it to have it but only if you are absolutely sure you're not going to need it (have a proper think). Also, I'd want to give you something for it..... money, beer, whiskey or something to charity (plus postage)?
 
I haven't seen anyone use a proper earth electrode tester on site since the 1990s

To be honest I don't think any new sparks would even know what to do with one

This video should help any such new spark ....

 
We have thunder and lightning here.... however, I have a new toy and have just been in my garden to experiment! Popped my spare 5/8" rod into the ground about 9", positioned the potential and current electrode correctly (in the pouring rain with a smile on my face) and pressed play! 180ohms.

I then hammered in it to about 15" and it went down to 96ohms.

This is all very exciting!

I darn't hammer it in any further as I did that in my garden as a practise when I first started out some years back (thinking I could just pull it out afterwards) and I had to dig a big hole to get it back out.
 

Reply to Why the need for an earth spike test kit? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
953

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top