sjm
Following on from a post a week or so ago about why not just wire to downlights in T+E I've attached the following photos.
I found these when called to an existing customer to locate a fault with the lights in their flat.
The installation was done 3 years ago, not by me I hasten to add.
What has happened is that the downlights have been covered in insulation by Bob The Builder. Although these particular JCC fireguard fittings do say in the instructions that they can be loosely covered with insulation if required by building regs.
My customer has then placed chipboard on top of the insulation in order to store things in the loft.
So although the electrician may not have known about the insulation plus the chipboard combination which has lead to the burning of the T+E, if he had followed best practice and used HR flex for the connection to the downlights then IMHO this wouldn't have happened.
Also I think he should have put some protection over the downlights as the loft was quite likely to be used for storage, the area of installation is right next to the loft hatch.
Your opinions would be appreciated as I've been asked to write a report for my customer. I have told them that the installation is NOT against the regulations, as such, but is IMO poor practice. I have also told them that their use of chipboard over the top of the insulation has contributed greatly to the problem.
So what do you guys think?
Thanks in advance.
Steve
I found these when called to an existing customer to locate a fault with the lights in their flat.
The installation was done 3 years ago, not by me I hasten to add.
What has happened is that the downlights have been covered in insulation by Bob The Builder. Although these particular JCC fireguard fittings do say in the instructions that they can be loosely covered with insulation if required by building regs.
My customer has then placed chipboard on top of the insulation in order to store things in the loft.
So although the electrician may not have known about the insulation plus the chipboard combination which has lead to the burning of the T+E, if he had followed best practice and used HR flex for the connection to the downlights then IMHO this wouldn't have happened.
Also I think he should have put some protection over the downlights as the loft was quite likely to be used for storage, the area of installation is right next to the loft hatch.
Your opinions would be appreciated as I've been asked to write a report for my customer. I have told them that the installation is NOT against the regulations, as such, but is IMO poor practice. I have also told them that their use of chipboard over the top of the insulation has contributed greatly to the problem.
So what do you guys think?
Thanks in advance.
Steve