well thats why its all galvanised so it does not deteriorate over time

It is only the coating that is galvanised, when you cut the conduit and then thread it you are exposing it to future corrosion.That is why you are supposed to paint the joint with galvofloid paint after.
 
Last edited:
Which is why you carry out PIRs.

If you rely on a seperate cpc in steel conduit how do you test it?
In theory you need to drop every socket & light on that circuit to seperate the cpc from the conduit otherwise you will pick up parallel pathes through the conduit.
So if you had a break in the cpc you would not pick this up as you would get a reading through the conduit.

If however you were relying on the conduit then all you would need to do is a long lead test.

But there is no guarantee that a PIR will be carried out....the reason why CPC's started to be installed in mechanical systems was simply to ensure that continuity is maintained in the event of corrosion. I guess in theory you are correct about separating the cpc and mechanical for testing...but in practice does it really matter?? as long as there is a low resistance R1R2 to the furthest point on the circuit I'm not gonna lose any sleep.
 
It is only the coating that is galvanised, when you cut the conduit and then thread it you are exposing it to future corrosion.That is why you are supposed to paint the joint with galvofloid paint after.
the only time ive ever been asked to paint joints is on the london underground and one hospital i worked in but i always make a point of painting weather im asked to or not
 
Your Zs value has to be low enough so that the MCB trips within the correct time in the event of a short circuit. (It is not really connected with an RCD tripping in the event of an earth fault and the trip times you get when rcd testing) If a Zs is too high then you do not get a high enough PFC to operate the overcurrent device (fuse/mcb) within the correct time. You can look those values up in appendix 2 of the OSG. However if your Zs is too low then the PFC could be so big as to cause you to have to upgrade to components with a higher breaking capacity.

edit : had not realised when writing Sintra has already addressed part of my answer (was on page 2)



there would be no need to upgrade components in a domestic installation as main fuse covers this eventuality
 
there would be no need to upgrade components in a domestic installation as main fuse covers this eventuality

I'm obviously no expert but think you might be wrong in this case if i have under stood things properly.
If Zs was less than 0.038ohms (probably pretty unlikely) then the PFC would be greater than 6kA for a fraction of a second. The mcb of that circuit would then trip. However, for that fraction of a second the huge current could be expected to damage any components that had a lower breaking capacity. If for example the breaking capacity of the mcb was 10 kA you would expect it to survive the dead short and you'd be able to reset it, but anything with a 6kA capacity would be damaged and need replacing.
I didn't think the main fuse comes into it.
Would welcome any other opinions as to whether i am right or wrong .
 
I recently did a PIR on a school with some old crabtree C50 mcb's with a 3ka rating and a measured PSC of over 5ka...I attributed a code 2 but our NIC inspector said as long as the rating of the enclosure exceeded the measured PSC it was acceptable.
 
I recently did a PIR on a school with some old crabtree C50 mcb's with a 3ka rating and a measured PSC of over 5ka...I attributed a code 2 but our NIC inspector said as long as the rating of the enclosure exceeded the measured PSC it was acceptable.

Cheers wirepuller - In other words are they saying that in the event of a dead short those mcbs might be wrecked but because they are in an enclosure with a higher rating that someone standing close by would be safe?
 
Last edited by a moderator:
Cheers wirepuller - In other words are they saying that in the event of a dead short those mcbs might be wrecked but because they are in an enclosure with a higher rating that someone standing close by would be safe?

Do you know if ordinary switches in a lighting circuit are given a short circuit withstand capacity or is that info hidden away inside the BS-EN number?

Agree it is not the enclosure that is protecting the circuit but the CPD.
 
Cheers wirepuller - In other words are they saying that in the event of a dead short those mcbs might be wrecked but because they are in an enclosure with a higher rating that someone standing close by would be safe?

Hi Mate,
Thats the gist of it....but I dont buy it....to my way of thinking if a 3ka mcb may be subjected to over 5ka that is not acceptable.....we changed the affected DB's for 10ka rated mcb's.
 
i am suprised nobody has also mentioned Zs x Idelta n < 50v

this is so in the event of a fault to earth the axtranious conductive parts have a fault voltage less than 50v
 
I recently did a PIR on a school with some old crabtree C50 mcb's with a 3ka rating and a measured PSC of over 5ka...

Have a look at paragraph 3 of 536.1 in the BRB. This is where the allowance of lower breaking capacaties upstream are discussed, with reference to higher ones downstream.
 

Reply to Why zs cannot be too big? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Had this before, found by the DNO to be a corroded fuse carrier on a pole mounted fuse on their LV network
Replies
1
Views
723
I am a landlord/owner of a flat. I am just about to spur off nearby sockets to provide the additional 24hr supply to new Dimplex Quantum storage...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top