What if your Zs is too high yet your trip times comply?
Zs is less or equal to Uo/Ia and Ze = Zs + (R1 + R2)
i still belive that a mechanical earth ie conduite trunking is a better fault path than 2.5 4mm cpc on lighting and power circuts it was ok 20 years ago and i still get lower readings wen i test itThe lower the Zs then the higher the fault current, the higher the fault current the faster the protective device will operate.
i still belive that a mechanical earth ie conduite trunking is a better fault path than 2.5 4mm cpc on lighting and power circuts it was ok 20 years ago and i still get lower readings wen i test it
i always test both any wayc pc and mechanical i disconnect all metal work fly leads etc take a reading on the cpc then re connect fly leads metal work and test again so wat is the point in running cpcs in a conduite trunking insatalltionProbably because you are getting parallel paths
What if your Zs is too high yet your trip times comply?
For instance say on a consumer unit upgrade, and what can be done to rectify this?
i always test both any wayc pc and mechanical i disconnect all metal work fly leads etc take a reading on the cpc then re connect fly leads metal work and test again so wat is the point in running cpcs in a conduite trunking insatalltion
The point is that steel conduit and trunking is liable to corrosion at joints and is very dependant on a high standard of workmanship for good electrical continuity. Thus in the long term a mechanical cpc may be subject to a deterioration in the continuity.
well thats why its all galvanised so it does not deteriorate over timeThe point is that steel conduit and trunking is liable to corrosion at joints and is very dependant on a high standard of workmanship for good electrical continuity. Thus in the long term a mechanical cpc may be subject to a deterioration in the continuity.
well thats why its all galvanised so it does not deteriorate over time
Which is why you carry out PIRs.
If you rely on a seperate cpc in steel conduit how do you test it?
In theory you need to drop every socket & light on that circuit to seperate the cpc from the conduit otherwise you will pick up parallel pathes through the conduit.
So if you had a break in the cpc you would not pick this up as you would get a reading through the conduit.
If however you were relying on the conduit then all you would need to do is a long lead test.
the only time ive ever been asked to paint joints is on the london underground and one hospital i worked in but i always make a point of painting weather im asked to or notIt is only the coating that is galvanised, when you cut the conduit and then thread it you are exposing it to future corrosion.That is why you are supposed to paint the joint with galvofloid paint after.
Your Zs value has to be low enough so that the MCB trips within the correct time in the event of a short circuit. (It is not really connected with an RCD tripping in the event of an earth fault and the trip times you get when rcd testing) If a Zs is too high then you do not get a high enough PFC to operate the overcurrent device (fuse/mcb) within the correct time. You can look those values up in appendix 2 of the OSG. However if your Zs is too low then the PFC could be so big as to cause you to have to upgrade to components with a higher breaking capacity.
edit : had not realised when writing Sintra has already addressed part of my answer (was on page 2)
there would be no need to upgrade components in a domestic installation as main fuse covers this eventuality
I recently did a PIR on a school with some old crabtree C50 mcb's with a 3ka rating and a measured PSC of over 5ka...I attributed a code 2 but our NIC inspector said as long as the rating of the enclosure exceeded the measured PSC it was acceptable.
Cheers wirepuller - In other words are they saying that in the event of a dead short those mcbs might be wrecked but because they are in an enclosure with a higher rating that someone standing close by would be safe?
Do you know if ordinary switches in a lighting circuit are given a short circuit withstand capacity or is that info hidden away inside the BS-EN number?
Cheers wirepuller - In other words are they saying that in the event of a dead short those mcbs might be wrecked but because they are in an enclosure with a higher rating that someone standing close by would be safe?
Whilst we are on the subject, has anyone seen an mcb destroyed, or damaged by too high a PFC?
I recently did a PIR on a school with some old crabtree C50 mcb's with a 3ka rating and a measured PSC of over 5ka...