Whilst testing the earth loop impedance on a circuit in a church the value given by the regular loop test is 1.74 but when doing it on non trip (with the neutral lead connected) we got >200.

Has anyone any ideas on what could cause that?

Thanks
 
Last edited by a moderator:
All 3 leads were connected. When doing the ZS on the board the 'trip' and 'no trip' loop vaules are the same so the problem is only on this circuit. We thought there might be a neutral problem but every other test carried out on that circuit is fine.

Could it be something to do with a high Ipf? We've tested part of the installation before and it was 4.2ka, but now between live and neutral is comes up as 14!
 

Reply to Wierd no trip impedance value in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
257
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
589
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top