Will an rcd operate on the secondary part of a transformer if the primary side is RCD protected?

Thanks in advance for your help
 
Can you draw a diagram of the arrangement and post it?
I am unsure if you are asking

A rcd feeding primary side, will a fault on secondary fed circuit trip it.

B if you have an rcd on the primary supply, will a second rcd on secondary output still work.
 
As well as the issue of isolated or not, the question of the effectiveness of an RCD on the output of an isolated transformer is also dependent on how it is earthed (if at all).

Some transformers (e.g. shaver supply) result in an IT arrangement and an RCD is of little use, but a typical 110V site transformer is 55-0-55 with the centre earthed, and for that an RCD is going to work even though 55V to earth is usually considered safe enough not to need it.

Usually is not always!
 
Can you draw a diagram of the arrangement and post it?
I am unsure if you are asking

A rcd feeding primary side, will a fault on secondary fed circuit trip it.

B if you have an rcd on the primary supply, will a second rcd on secondary output still work.

Not the best diagram aha
 

Attachments

  • [ElectriciansForums.net] Will an rcd operate
    A8E58E62-273C-4E2C-9699-04D682323F38.jpeg
    30.1 KB · Views: 31
OK, so try answering a few questions first to see if you can deduce the answers:

1) Is the transformer you sketched isolating on not?
2) What path for current in a RCD trips it?
3) To answer question (a) is your answer to #2 normally present in this arrangement?
4) Your question (b) has several aspects:
  • What is your definition of "not work"?
  • How might two RCD in series fail to meet the IET regulation 536.4.1.4?
  • Returning to your answer to #2, is that present in your diagram for the secondary circuit?
 
OK, so try answering a few questions first to see if you can deduce the answers:

1) Is the transformer you sketched isolating on not?
2) What path for current in a RCD trips it?
3) To answer question (a) is your answer to #2 normally present in this arrangement?
4) Your question (b) has several aspects:
  • What is your definition of "not work"?
  • How might two RCD in series fail to meet the IET regulation 536.4.1.4?
  • Returning to your answer to #2, is that present in your diagram for the secondary circuit?
OK, so try answering a few questions first to see if you can deduce the answers:

1) Is the transformer you sketched isolating on not?
2) What path for current in a RCD trips it?
3) To answer question (a) is your answer to #2 normally present in this arrangement?
4) Your question (b) has several aspects:
  • What is your definition of "not work"?
  • How might two RCD in series fail to meet the IET regulation 536.4.1.4?
  • Returning to your answer to #2, is that present in your diagram for the secondary circuit?

My understanding is it wouldn’t work as it has a separate live and neutral. So to rcd protect it we’d have to put an rcd downstream and change the upstream to a time delay to comply with regs
 

Reply to Will an rcd operate in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
275
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
652
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
825

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top