Hi guys
Testing today large country manor house/mansion today and had a issue with getting loop reading on no trip on my fluke 1653 mft. could only get a loop reading on high current. I can physically see that the earth is connected and I have a voltage present.
The installation briefly compromises of 2 phases incoming linked at source to make 3 phases ( awaiting new substation and 3 phase feed from dno.) TT system ,60947-2 incoperating S type rCD. changeover switch( set on mains) mains panel with 8x three phase sub feeds.
Nowhere on this installation can I get a no trip reading. all I get is greater then 2000 ohms but yet acceptable readings on high current.
The sub mains I can test on high but when it came to the final circuit's (all rcbo protected) would be easier on no trip.
Easier or not I would still like to know why I am not getting a loop on no trip so any help would be appreciated
Testing today large country manor house/mansion today and had a issue with getting loop reading on no trip on my fluke 1653 mft. could only get a loop reading on high current. I can physically see that the earth is connected and I have a voltage present.
The installation briefly compromises of 2 phases incoming linked at source to make 3 phases ( awaiting new substation and 3 phase feed from dno.) TT system ,60947-2 incoperating S type rCD. changeover switch( set on mains) mains panel with 8x three phase sub feeds.
Nowhere on this installation can I get a no trip reading. all I get is greater then 2000 ohms but yet acceptable readings on high current.
The sub mains I can test on high but when it came to the final circuit's (all rcbo protected) would be easier on no trip.
Easier or not I would still like to know why I am not getting a loop on no trip so any help would be appreciated