Hi guys

Testing today large country manor house/mansion today and had a issue with getting loop reading on no trip on my fluke 1653 mft. could only get a loop reading on high current. I can physically see that the earth is connected and I have a voltage present.

The installation briefly compromises of 2 phases incoming linked at source to make 3 phases ( awaiting new substation and 3 phase feed from dno.) TT system ,60947-2 incoperating S type rCD. changeover switch( set on mains) mains panel with 8x three phase sub feeds.

Nowhere on this installation can I get a no trip reading. all I get is greater then 2000 ohms but yet acceptable readings on high current.

The sub mains I can test on high but when it came to the final circuit's (all rcbo protected) would be easier on no trip.

Easier or not I would still like to know why I am not getting a loop on no trip so any help would be appreciated
 
No trip was tried at each Point and at a couple of the sub mains and still greater then 2000ohms

No trip was also tried with a different tester and same result.
 
on a TT system it might be that the reistance is too high for the no-trip test to pass the low current.
 

Reply to will only test loop on high current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
573
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
764
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
479
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
469

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top