Can this be done?
Hi
ALthough not good practice, is this acceptable? Its one of my first jobs!
double Cooker on 6mm 4.6Kw = 20 amp plus 5amp as it has a socket = 25amp
A spur from cooker to SFCU 5amp then down to fridge at 400w = 1.8amps
a spur from that SFCU upto another 5amp SFU to Feed Microwave 800w - 3.5amp
a spur from that SFCU upto another 3amp SFU to Feed cooker hood 205w with lights - 0.9amp
Basically there is only a cooker circuit on the wall of this small kitchen with integrated socket so space is limited.
Also the customer does not want the upstairs torn up due to refurbishment I cannot see anywhere it says that this is not acceptable, all cables will be 2.5mm except
first spur from cooker and each feed from the previous sfcu will go from the load side.
Does this make sense and viable?
I have included a crap diagram but should help, any thoughts appreciated. You mmay have to zoom in
http://i604.photobucket.com/albums/tt128/gdp-it/proposedcircuit.jpg
Many thanks
Hi
ALthough not good practice, is this acceptable? Its one of my first jobs!
double Cooker on 6mm 4.6Kw = 20 amp plus 5amp as it has a socket = 25amp
A spur from cooker to SFCU 5amp then down to fridge at 400w = 1.8amps
a spur from that SFCU upto another 5amp SFU to Feed Microwave 800w - 3.5amp
a spur from that SFCU upto another 3amp SFU to Feed cooker hood 205w with lights - 0.9amp
Basically there is only a cooker circuit on the wall of this small kitchen with integrated socket so space is limited.
Also the customer does not want the upstairs torn up due to refurbishment I cannot see anywhere it says that this is not acceptable, all cables will be 2.5mm except
first spur from cooker and each feed from the previous sfcu will go from the load side.
Does this make sense and viable?
I have included a crap diagram but should help, any thoughts appreciated. You mmay have to zoom in
http://i604.photobucket.com/albums/tt128/gdp-it/proposedcircuit.jpg
Many thanks