cyberjunction

Can this be done?
Hi
ALthough not good practice, is this acceptable? Its one of my first jobs!
double Cooker on 6mm 4.6Kw = 20 amp plus 5amp as it has a socket = 25amp

A spur from cooker to SFCU 5amp then down to fridge at 400w = 1.8amps

a spur from that SFCU upto another 5amp SFU to Feed Microwave 800w - 3.5amp

a spur from that SFCU upto another 3amp SFU to Feed cooker hood 205w with lights - 0.9amp

Basically there is only a cooker circuit on the wall of this small kitchen with integrated socket so space is limited.

Also the customer does not want the upstairs torn up due to refurbishment I cannot see anywhere it says that this is not acceptable, all cables will be 2.5mm except
first spur from cooker and each feed from the previous sfcu will go from the load side.

Does this make sense and viable?

I have included a crap diagram but should help, any thoughts appreciated. You mmay have to zoom in

http://i604.photobucket.com/albums/tt128/gdp-it/proposedcircuit.jpg


Many thanks
 
don't like it at all. other appliances could be plugged in , blowing your fuses. either extend the ring or run a separate radial at 16A for the appliances.
 
yeah. allowing for diversity on the cooker, 10A+3.3A = 13.3A ( ditch the incorporated S/O ) ... 16A or 20A MCB, then 16A radial for sockets. 32A MCB at CU.
 

Reply to Will this work? Input appreciated in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top