Winter park,fl
I'm a home owner, not an electrician. I have a window ac unit that draws 7.5amps. All I have in my garage is an outlet that's on a 20 amp breaker. Will 20 amp work or do I need to replace it with a 15amp Breaker?
the rating of the breaker should be less than the max. amperage of the cable it feeds, but greater than the load current. i.e. if the cable will carry > 20A, it's fine.
Could you explain to me how breakers work. 20 amp breaker on a 20amp outlet. The cord to my ac unit is 14awg. 14 awg can handle 20amps? And the ac uses 7.5 amps, wouldn't that destroy the ac unit since I have 20 amps going to it? Thank your help.
If it will make you feel better you can change the breaker to a 15 amp, since the FLA is only 7.5 amps. The breaker is there for 2 reasons with one being overcurrent protection and the other is for short circuit protection. Hope this helps
Reply to Window AC outlet in the UK Electrical Forum area at ElectriciansForums.net
An electrician installed a NEMA 6-20 20A 230V outlet in a surface box for me in my garage, on a dedicated 20A breaker. He was even kind enough to...