Hi everyone, prob seen this before can you wire outgoing circuits in 3 core flex??
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Wire in flex!!!Hi in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone, prob seen this before can you wire outgoing circuits in 3 core flex??
Depends on what type of cable he is thinking of using and what for Pete. Lets see if the OP answers my questions.
Hi thanks for replies
fed in 3c 1.5 flex
circuit runs in galv trunking and tray work
protected by 16a type b mcb
switched via a 20a contactor
not found what it's switching yet but most probably doing some stage lighting in the theatre area, on a rig
seems like theatre installation electricians just use what's on the van
It's an existing installation, just doing EICR, but not sure I would of used flex