I have an existing but unused 50A disconnect on the side of the house. It had been connected to an AC unit that got replaced. It has just 3 wires run to it - hot, hot, and ground. I want to repurpose it for an RV hookup, using a Nema 14-50R receptacle. However, that receptacle requires a neutral, which is not present in the disconnect. I know my RV also does not really use 220, but just 110, so a neutral will be required.
my question is: at the receptacle enclosure, can I tie the ground and neutral together, using the ground as a neutral as well?
if not, is it possible to “repurpose” one of the hot wires into a neutral, and just have this be a 110 circuit? (At which point I would use a TT-30 R receptacle). At the service panel, I would change to a single pole breaker, and move the old hot wire to the neutral bus. But if that is allowed, since the wire color is different, should I wrap it in white tape or something? And would it matter if it were the red or black wire at that point?
for other reasons, I really prefer the 14-50R outlet if that is possible!
thanks for the help!
my question is: at the receptacle enclosure, can I tie the ground and neutral together, using the ground as a neutral as well?
if not, is it possible to “repurpose” one of the hot wires into a neutral, and just have this be a 110 circuit? (At which point I would use a TT-30 R receptacle). At the service panel, I would change to a single pole breaker, and move the old hot wire to the neutral bus. But if that is allowed, since the wire color is different, should I wrap it in white tape or something? And would it matter if it were the red or black wire at that point?