Wiring a garage subpanel with a packed house panel. Simple answer (I think). | on ElectriciansForums

Discuss Wiring a garage subpanel with a packed house panel. Simple answer (I think). in the UK Electrical Forum area at ElectriciansForums.net

JonathanB

DIY
Joined
Jun 7, 2021
Messages
1
Reaction score
0
Location
Clinton, CT
I have charged ahead with a small subpanel installation in a detached garage I am converting to a light-duty shop. The setup is simple, but I have been stymied by a final step. Hoping someone can help.

Old setup was a buried 12-2 wire from a 20a breaker in the house panel (100A) connecting to one circuit (no breaker) powering two outlets, a light bulb, and a garage door opener.
In the house main panel, there is one and only one available opening in the box for a new breaker.

The new garage panel has three circuits: one 15A for LED lights and the door opener, and (2) 20A for two separate runs of outlets (5 outlets per run in three boxes)

The new wire to the garage is in conduit and is 8-2. Within the garage sub-panel, and since I am not running 220, I connected the hot to both sides of the bus using s short black jumper wire. This allowed me to mount the three breakers side-by-side rather than separated by knockouts and made both sides of the bus hot.

The neutral is connected to a neutral bus bar and and I installed a separate ground bus, which has a 4ga wire running to a fully buried grounding rod.

I have temporarily (waiting for the right breaker) wired the house-panel wires to a 20A breaker, which has the black wire in the load terminal. The white wire (8ga) is on the neutral bus, and the ground on the ground bus.

My idea was a 40A breaker in the house. But if I want full amperage connected through the wiring to the garage panel, what is the correct way to install (wire) the breaker in the house? A two-gang 40A breaker takes two spaces, but I think I can't connect the white wire to one of the load terminals on that, or that will connect to the neutral bus in the garage panel. I also have a tandem breaker, but that seems to have the same issue. I think I run the black wire to a single-gang, single-pole 40A breaker and connect the white wire to the neutral bus in the house panel, yes? That will run the entirety of the circuit (40A) through a single black wire.

Related, what amperage should the breaker you suggest be? Single pole 40A?

Notes:

I do have space in the panel for either a single-gang or two-gang (two pole?) breaker in the main panel.
I have a twin (duplex?) (tandem?) breaker that is two poles and 20a per pole. I also have a two-gang, two pole 40a per pole. Do either of these work?
All of the outlets test out properly using a plug in tester, including the proper functioning of GFIs.

Thanks in advance!

Signed,

ALMOST THERE in Connecticut.
 
I have charged ahead with a small subpanel installation in a detached garage I am converting to a light-duty shop. The setup is simple, but I have been stymied by a final step. Hoping someone can help.

Old setup was a buried 12-2 wire from a 20a breaker in the house panel (100A) connecting to one circuit (no breaker) powering two outlets, a light bulb, and a garage door opener.
In the house main panel, there is one and only one available opening in the box for a new breaker.

The new garage panel has three circuits: one 15A for LED lights and the door opener, and (2) 20A for two separate runs of outlets (5 outlets per run in three boxes)

The new wire to the garage is in conduit and is 8-2. Within the garage sub-panel, and since I am not running 220, I connected the hot to both sides of the bus using s short black jumper wire. This allowed me to mount the three breakers side-by-side rather than separated by knockouts and made both sides of the bus hot.

The neutral is connected to a neutral bus bar and and I installed a separate ground bus, which has a 4ga wire running to a fully buried grounding rod.

I have temporarily (waiting for the right breaker) wired the house-panel wires to a 20A breaker, which has the black wire in the load terminal. The white wire (8ga) is on the neutral bus, and the ground on the ground bus.

My idea was a 40A breaker in the house. But if I want full amperage connected through the wiring to the garage panel, what is the correct way to install (wire) the breaker in the house? A two-gang 40A breaker takes two spaces, but I think I can't connect the white wire to one of the load terminals on that, or that will connect to the neutral bus in the garage panel. I also have a tandem breaker, but that seems to have the same issue. I think I run the black wire to a single-gang, single-pole 40A breaker and connect the white wire to the neutral bus in the house panel, yes? That will run the entirety of the circuit (40A) through a single black wire.

Related, what amperage should the breaker you suggest be? Single pole 40A?

Notes:

I do have space in the panel for either a single-gang or two-gang (two pole?) breaker in the main panel.
I have a twin (duplex?) (tandem?) breaker that is two poles and 20a per pole. I also have a two-gang, two pole 40a per pole. Do either of these work?
All of the outlets test out properly using a plug in tester, including the proper functioning of GFIs.

Thanks in advance!

Signed,

ALMOST THERE in Connecticut.
My friend first off you need 8/3 with ground wiring and it should be installed on a 40 amp double pole breaker in your main panel. The wire should have a black, red, white, and a ground wire. The black needs to hook to one screw and the red hooks to the other screw on the 40 amp double pole breaker. The white and ground have to be separated at this point so in your sub panel you will probably have to add a ground bar. You do not need the ground bar at the garage, that’s why by code you have to have a 4 wire cable not 3 a wire cable. You are going to need help with this project from an experienced electrician. Good luck
 

Reply to Wiring a garage subpanel with a packed house panel. Simple answer (I think). in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
645

Similar threads

  • Question
Yes you will need to install # 4 wiring times 4 for your 2 hots, 1 neutral and 1 equipment ground. As for keeping the grounds and neutrals...
Replies
3
Views
1K
  • Question
So this was resolved. I used a line tester to see if I had power across the breaker on the main box in the house. Breaker tested fine. Then I...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top