Wiring a motor | on ElectriciansForums
Discuss Wiring a motor in the UK Electrical Forum area at ElectriciansForums.net
Scrappy11
Hi all, newbie here with an opening post/problem
I've just acquired a metal lathe, and to cut a long story sideways I've been having problems wiring the motor to a switch box. The FLA reading on the motor says 3.75, so I bought a switch box with an overload amp rating of 2.5-4 amps (assuming that would be good for the motor). When I plug the motor directly into the socket, there's no problem with the fusebox in the garage (where it's set up), however when I wired it up to a switch box, it's constantly tripping the RCD.
So basically my question really is - where the hell am I going wrong?
ANY advice/ideas/insight on the matter would be massively appreciated, any details just ask.
Ta
Dom
ok, this should be everything:
supply voltage is a normal 240v socket
(on the motor)
220-240 volts
single phase
3.54 (sorry not 3.75) F.L. Amps
0.5 HP
Class E (I don't know if this is relevant)
(switch/starter)
DOL Single Phase Motor Starter c/w Overload of Choice
2.5-4 Amp overload
240 V contractor coil
here are some pics of the motor, inside the starter and inside the starter housing.
[ElectriciansForums.net] Wiring a motor
You need current flowing through all 3 contacts as per Tony's diagram, otherwise the O/L will see an imbalance and trip.
However, you say that it is tripping an RCD in a switch box? but not on the garage fuseboard. Please explain in more detail how your supply is set up.
I have a separate fusebox for the garage. Basically the house has a main fusebox (standard), but a separate wire runs out of the fusebox into a secondary fusebox for the garage since it's detached from the house. I think (I'm not pro, I've just worked this out for myself) that maybe it's drawing too much power? The motor is fine when plugged into a normal socket, it's just when I wire it to the switch/starter that it trips the RCD in the garage and thus the main switch in the house.
If the motor runs fine when plugged in to a socket then there's a good chance it's you wiring of the DOL starter.
It might be worth a quick IR test of the windings, if they're okay (>2Mohms) then wire up as per Tony's diagram.
Reply to Wiring a motor in the UK Electrical Forum area at ElectriciansForums.net
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks
I would have to agree with @James to hire an electrician to measure the voltage coming in to the panel. If you have 240vac phase to phase then you...