hi all, i am about to wire up my shed, its integral to the property, the meter cupboards are next to the shed so i can run a supply through the wall. there will 4 2 gang sockets, bulk head in there and a switched spur for outside light. i'm going to run out from the rcd side of the board using a 32amp mcb. the shed will be wired in singles, trunking and conduit. is this ok to do? was talking to a mate and he was a little unsure as to whether this is ok, i cant see any reason as to why not. is it best to just use the mcb on the rcd side of the board or fit an rcbo instead? this will be used as part of the elecsa assessment.

thanks for any suggetions
 
you can run from CU MCB a ring (32A)or radial (16A) RCD protcted at CU, FCU in shed for internal and extenal lights
 
Last edited:
if you use 32A then your circuit in shed must be a ring. if you want to have it as a radial use a 16A. whichever you use, must not share breaker with another circuit. check your potential load on sockets to see if you need a ring. alternatively, you could run 4mm T/E radial.but rem to FCU at 5A for lighting
 
Last edited:

Reply to wiring in shed in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
207
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

You should have no problems with what you want but even if you install conduit the cable still needs to be UF cable which is approved for under...
Replies
1
Views
741
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
868

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top