Wiring my 8 pole motor | on ElectriciansForums
Discuss Wiring my 8 pole motor in the The Welcome Forum area at ElectriciansForums.net
Jacus
New forest hampshire
Hi everyone
I'm new to this forum page. I live in the new forest in Hampshire and I'm in need of some electrical support please.
I bought a new 8 pole induction motor and I haven't a clue how to wire it up to the mains. I need the motor to turn anti clockwise if possible as I'm working with my kids to make a plastic extruder machine.
I will attach some photos to give you guys an idea. Any advice will be much appreciated. !
Your motor is wired in delta.
Connect your 3 live wires to each of the 3 terminals U1, V1 & W1.
The 2 blue wires are probably for a thermal overload.
This would be wired in conjunction with a contactor, to cut power to the motor if it over heats.
Hi spinlondon
Thanks for the message. With regards to wiring the 3 live wires into U1 V1 & W1....can I wire them into any of the ports? Are we talking about the normal 3 wires...blue , yellow and brown?
Sorry if the questions sound a bit daft but I don't want to cause an electrical fire or issue.
If you say my wiring is Delta, does that have anything to do with the rotation?
Many thanks
The motor is shown wired in Star configuration for a 400v 3ph supply. Connect the three phase 400v supply via a suitable starter to the terminals marked U1, V1 & W1.
The two blue wires are a thermistor, this will need a seperate Thermistor relay that will detect the change in resistance of the thermistors if the motor overheats. This relay then trips the motor starter.
If you wire it up and it goes the wrong way, simply swap two over any two of the incoming phases.
Hi spinlondon
Many thanks
Aplogies if you do, but based on your responses. Do you understand that this motor requires a 3 phase supply?
You won't have that at home.
It will also require a DOL starter with a 0.63A range thermal overload relay.
You have a motor which will operate in Delta at 230v or Star at 400v. Unfortunately both these modes of connection whether 230v Star or 400v Delta require a three phase supply. It sounds like you only have 230v single phase and hence it will not operate.
Not sure how much torque your application requires, but if you cant return the motor you can actually make it run on a single phase supply simply using 2 capacitors.
This may work in a classroom but for practical applications it is not really feasible.
Reply to Wiring my 8 pole motor in the The Welcome Forum area at ElectriciansForums.net
I would agree that the motor is by far the best part to replace. if it is powered and not turning then it is broken. Keep it simple!
I know this post is nearly 6months old but its essential for future readers of this thread to be reminded here what the OP is suggesting is not an...
Darkwood