I have a new oven and hob ( 3.4kw and 6kw) to replace old cooker.
The current wiring is 45amp mcb at CU and 6mm cable to double pole switch at cooker wall.
The oven and hob add up to 9.4kw. Can i just use a dual appliance plate and wire them both into the current wiring with switch and 45amp mcb??:confused:
Or do I have to have a fused protection for each ie 16amp fuse and 30amp fuse??
Running a seperate wire back to the cunsumer unit will ba a major task as new floor etc
 
You can use the one control providing both units are rated between 15 and 50 amps both would also have to be within 2 mtrs of switch.


Hope that helps



Chris
 
Both are within 2mtrs of switch.
Will the 45amp fuse be too much if one item say the oven has a fault?
 
The breaker is to protect the cable.

45 A is too large for 6mm cable. (So the regs say, but not a really big problem)

Your appliances together are

9.4/230=40.87 amps
40.87-10=30.87amps
therefore
30.87*30%=9.26amps
9.26+10=19.26amps

So to be correct pop a 32 amp breaker in which will be more than enough.

A dual appliance plate will be fine.
 
Last edited:
You should also consider the length of the run and install method as that could derate your cable. It might also be worth having a word with the client as to whether or not they expect it to have regular heavy use, if not the diversity calc above is fine.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Wiring oven and hob from one mcb
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Rayelect,
Last reply from
pushrod,
Replies
4
Views
4,735

Advert

Back
Top