R

Rayelect

I have a new oven and hob ( 3.4kw and 6kw) to replace old cooker.
The current wiring is 45amp mcb at CU and 6mm cable to double pole switch at cooker wall.
The oven and hob add up to 9.4kw. Can i just use a dual appliance plate and wire them both into the current wiring with switch and 45amp mcb??:confused:
Or do I have to have a fused protection for each ie 16amp fuse and 30amp fuse??
Running a seperate wire back to the cunsumer unit will ba a major task as new floor etc
 
You can use the one control providing both units are rated between 15 and 50 amps both would also have to be within 2 mtrs of switch.


Hope that helps



Chris
 
The breaker is to protect the cable.

45 A is too large for 6mm cable. (So the regs say, but not a really big problem)

Your appliances together are

9.4/230=40.87 amps
40.87-10=30.87amps
therefore
30.87*30%=9.26amps
9.26+10=19.26amps

So to be correct pop a 32 amp breaker in which will be more than enough.

A dual appliance plate will be fine.
 
Last edited:
You should also consider the length of the run and install method as that could derate your cable. It might also be worth having a word with the client as to whether or not they expect it to have regular heavy use, if not the diversity calc above is fine.
 

Reply to Wiring oven and hob from one mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
558
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
925

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
565
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top