Wiring sensors | on ElectriciansForums

Discuss Wiring sensors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

N

nabba

Hi, I'm wiring lights about 20 via trunking in singles to loop in boxes , because the room is large I will need to position at least 2 or 3 sensors so either one will bring lights on ... Any advice on the wiring them pls ? I realise first off , live neutral earth to supply the sensor what do I take to the other one to incorporate it then obviously switch wire to lights its just the sensors im itchin my head at ... been that long time since did this sure it's simple just need direction
Thanks ...
 
Hi , thanks for getting back. Yes pir's this is the thing parellel ?? so live neutral earth from the board into first pir then would it be live neutral earth to the next one and a switch wire so that either pir switches they will all come on is this right ...? Parellel always confuses me in lighting
Thanks again .
 
Yes, line, neutral, earth and a switch live need to be taken between each pir.

What type of light fittings are you switching, make sure the PIRs can switch the required load.
 
Thanks again, I think at the moment it's going to be 600x600 square fluorescents placed into a new office refurb grid ceiling ,... Not sure what the wattage is on each one yet as drawings not arrived ...
 
you do need to know the load.............. to condier zs value and vd... you could break the room up say first 10m the lights come on walk a little further and the next set come on
 

Reply to Wiring sensors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

That will work fine as long as the Pirs use relay switching, some don't.
Replies
2
Views
518
  • Question
very few capacitive sensors are suitable for direct insertion into a safety circuit. the only ones that i have ever come across have there own...
Replies
1
Views
469

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top