Good evening all

What do you guys write under the following on your EICR forms

1. Extend of the electrical installation covered by this report

2. Agreeded limitations

3. Operational limitations

Cheers
[automerge]1591294257[/automerge]
In a domestic property
 
Last edited:
Good evening all

What do you guys write under the following on your EICR forms

1. Extend of the electrical installation covered by this report What it says. If the EICR covers the entire installation then state that, if it only covers the house and not the garage state that

2. Agreeded limitations This is limitations agreed with the client. Technically you would discuss the extent of testing and inspection with the client prior to work commencing. If the client decides they want to save money by omitting the R1+R2 test that would be an agreed limitation.

3. Operational limitations This would be (for example) where access to a part of the installation was not possible at the time of the inspection, perhaps because of a safety issue if the correct access equipment was not available. This would be stated in this section

Cheers
[automerge]1591294257[/automerge]
In a domestic property
My answers in red
 
1 write down what you agreed to inspected and test with the customer For example. inspection of all identified fix wiring and 25 % of accessories within the installation

2 write down the limitations you agreed with the customer before hand. For example the customer does not want you to do any inspection of the shed write that down

3 write down any limitations you come across during the inspection. For example. limited testing and inspection of socket in garage due to the garage full of boxes .
 

Reply to Wording on EICR in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
291
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top