r1: 1.15
r2: 1.80
rn: 1.15
r1r2 0.69
To work out the length of a ring in 2.5mm twin would this be correct
0.69/(19.51/1000) = 35m
or would you use the r1r2 before you divide it by 4?
The r1 and r2 values you have are both measured end-end on the RFC, so if using tables of R1+R2 (such as Table I1 in the OSG) then you would add them and divide by the table value:
length = (r1 + r2) / R1plusR2perLength = (1.15 + 1.80) / (19.51/1000)
So it would go something like this?
2.95 / 0.01951 = 151 meters
so this to work out the voltage drop it would then be
Voltage Drop = ( mV/A/m ) x L x Ib / 1000
18 x 151 x 32 / 4 = 21744 / 1000 = 21 volts
does not comply with voltage drop
To be pedantric, you can't work out the length of a ring, only the circumference,
When calculating the length of an existing ring, for simplicity and accuracy I prefer to use the resistance of just one of the live conductors for the calculation.
r2 is not always accurately measured, due to different sized CPCs, and parallel paths, so including it in the calculation can lead to inaccuracies. The live conductors shouldn't have parallel paths (assuming equipment is not in circuit), so if the measured r1 and rN are identical, then you can be fairly confident that both live conductors are continuous and without loose connections.
From OSG table I1, the resistance of a 2.5mm2 conductor is 0.00741 ohms/m at 20 deg C.
1.15 / 0.00741 = 155.2 m
Note that I prefer to use ohms rather than milliohms for the resistance/m part of the calculation, I find it simpler that way.
Yes. Though see @Pretty Mouth comment about accuracy on typical measured r2
Not quite, but a quick check in the OSG Table 7.1(ii) shows the max length is 106m for 2.5mm so you are right it will fail.
The drop for a RFC is not end-end as it is for a radial.
Starting with the Zs situation, in the case of the RFC the worst-case R1+R2 seen at a socket is half-way around the ring, closer to either end and you have a shorter cable and less drop. Note that you might not actually have a socket at the half-way point!
But if you did, then you have two legs feeding it, each of L/2 so they have voltage (r1+r2)/2 and as those two are in parallel your R1+R2 would be computed from (r1+r2)/4 and adding your Ze you get Zs
Volt drop follows a similar logic, in effect you have two parallel paths so your L & N drop is from end-end divided by four to account for being half-way, and those in parallel. You seem to be doing this but the way you write out the equation is slightly odd, as you divide the current by 4 which achieves the same, but is not really reflecting the L/4 reasoning.
But the VD for a RFC and similar has the further complication that your load is not usually in one place but spread out over multiple sockets, similar to a light circuit, but for normal computation you can assume the worst-case is 26A at the mid-point from two 13A sockets at full load (which also ties in with OSG table 7.1(i) of assumed loads).
If your loads are all small compared to the OCPD as in the lighting case then you typically assume they are evenly spread out so the total load can be assigned to half-way on the cable for VD (i.e. half the VD compared to an end-of-circuit radial load like a cooker, immersion heater, etc).
For Zs it is always worst-case at end of radial, or RFC mid-point, that you use for checking circuit protection.
Your voltage drop calculation is about right. A slightly different way to go about it:
The most onerous conditions for voltage drop on the ring, is the full 32A load at the mid-point of the ring. As the resistance of both legs between this mid-point and the CU is identical, half of this current will flow through one leg, half down the other.
So, 16A flows from the CU, through the line conductor of one leg to the mid-point, then through the N of that leg back to the CU. Using V=IR, we can calculate the voltage drop for this current flowing through this resistance.
Resistance of one leg = (r1 /2) + (rN /2) = 1.15 ohms.
At the full 70 deg C operating temperature, this resistance would be: 1.15 x 1.2 = 1.38 ohms
V = IR = 16 x 1.38 = 22.34 V
For comparison, let's use your way of calculating voltage drop, with the 155.2m that I arrived at previously:
18 x 155.2 x 32 / 4 / 1000 = 22.3488 V
Same result, slightly different way of getting there.
Note that the standard ring final in the OSG uses a design current of 26A. I believe it also uses the correction factor from p429 of the regs to arrive at a 106m long circuit.
I'm getting there with it but a drop of 22 volts on a rfc is a fail of vd?
So if you used a 16amp mcb on a rfc the formula would stay the same? But in the above case the vd would then comply
What would happen if you exceed VD than say less than 10%
Yes, the regs say 5% max which is 11.5V
Yes and no.
If it was designed for 16A of typical load then it would meet the VD requirement, and without any special design information you would assume that a 16A MCB means it is designed for a 16A load.
However, if you need more than 16A because it covers a lot of rooms with various significant loads then you will simply trip the MCB. So in that case you have failed to design for the required use.
For something like a set of sockets what constitutes the correct design load is not hard and fast. If you look in the OSG it has typical coverage area for 20A radial, 32A radial, and 32A RFC circuits and for a lot of cases that is your reasonable usage.
However, if you have a non-domestic system it can go far in the other directions:
  • For example you might have 6 * 32A sockets in a factory but only one mobile item that uses them so you can design for 32A.
  • Or you might find you have 6 * 13A sockets in a commercial kitchen and they all get loaded to pretty close max at the same time so a 32A RFC is not enough and you need two 32A radials or similar.
It depends, and in many cases not a lot. The ESQCR states that the nominal supply voltage should be 230V -6% +10% which is 216V to 253V and if your combination of supply voltage and circuit VD keeps the appliance voltage within that range then all equipment should work normally.
If the voltage drops very low then some equipment will malfunction and in unusual cases even be damaged by out of range operation.
In reality if you have found an unacceptably large RFC as this appears to be you need to make a judgement call about what to do. The first aspect is if it is safe or not, and that comes down the protection being able to act quickly. In today's "RCD everything" situation that should be simple but many folks like myself like to see a sporting chance that it could disconnect on the OCPD side safely, which comes down to the worst-case Zs and the MCB choice. That depends on your R1+R2 as well as Ze, so it is more than just the VD value (but they are closely related as VD depends on R1 of course).
The second aspect of the judgement is if the circuit is likely to cause trouble, and if it has been used for years without complaint then you have a reasonable answer "no". For example, you might have a very long RFC feeding a handful of sockets in an attic conversion, in which case are you likely to need 26A for any normal activity?
So while it is not compliant, if it is unlikely to lead to problems then I would leave it with a note to that effect. The only way to serve more current is to rewire some or all in 4mm or similar, dropping the MCB to 20A or 16A might make it design-consistent but it does not help the person who needs any more current.
Yes and no.
Thanks for the reply its educational to say the least.
I found a ring of 151 meters and one of 135 meters so they are both over the range for VD
The longest one feeds two bedrooms and the shorter one feeds a front room and hallway
Leaving them on 32 amps does not sit well with me.
They meet the Zs requirement.
With a ring on 32 amps you have a design current of 26 amps
If the ring was on a 25amp breaker or 20amp breaker would the design current be 25amps and 20 amps or would it reduced like the 32amps is reduced to 26amps
If I were you I would get some realistic loading figures. It's unlikely a circuit feeding two bedrooms will get anywhere close to 26A in this day and age. It's more likely going to be less then 2kW which is 8.3A which conveniently (using PrettyMouths approach) is a voltage drop of 11.5v I believe which is the absolute maximum.
So you need to establish the loads that are used in the rooms, how much and how they overlap to establish an actual predicted maximum. Not an absolute design maximum.
If strictly complying with regs, a ring final circuit can only have a 30 amp or 32 amp protective device.
You are allowed to increase the cable CSA beyond 2.5 sq mm though, to reduce your resistance and hence volt drop.
In your case if Zs is met, you have to ask how much is likely to be drawn by two bedrooms or a front room.
If it's a freezing 14th century mansion with no central heating and you are expecting a fan heater, a hair dryer and an electric blanket in both bedrooms to be on simultaneously then you might have a point, or e.g. student rooms with a microwave and air fryer in each, but chances are it will be an LED bedside light and a phone charger?
I'm not saying ignore volt drop requirements, but you do have to be realistic.
I can't tell if this is a real life example, or a college exam questions, as I first assumed? Do tell us the whole story!
The breaker is there for overload and fault protection. The only relation the breaker has with design current, is that the design current should be no greater than its rating. Lowering the breaker rating doesn't lower the design current however - you design the circuit and protective device(s) based on the design current, not the other way round.
In this case, you're dealing with existing circuits. @pc1966 and @SparkyChick have covered this nicely in the last few posts, the only things I'll add are:
It is unlikely that the circuits will be heavily loaded for any length of time, if ever.
Even if they are, the supply voltage, in my experience, usually measures 240V or more, which is a large margin of error over the lower acceptable limit of 216V.
Personally, I wouldn't be concerned with these circuits.
What is it you are actually doing?
Learning I have done a level 2 and 3 and working on my NVQ.
I have started working with my dad who is QS and old spark and he brought a new property and has let me test it to get some real world experience before he tests its. ( its empty I cant hurt anyone )
why cant you comply with the regs if a ring is not on 30 or 32 amps seems strange
Its a fairly new building
so at 32 amps the volt drop would be
18x26x151/4 = 17667 / 1000
= 17 volts which is about 7.5% volts dropped in the bedrooms
18x26x133/4 = 15561/1000
=15.5 volts dropped which is about 6.75% volts dropped in the front room
im just asking realistically in the real world is that a problem where you would rewire in 4mm
In brief, a ring final circut is an exception to the normal rule than the cable can carry at least as much current as the protective device.
The one and only reg (look up 433.1.204) sets out the conditions you can break the normal rule, and part of those conditions are a 30 or 32 amp device.
It's basically saying that if the load current is unlikely to exceed the CCC of the cable for long periods, and the cable can carry 20 amps, it is deemed to comply.
(Much older regs versions had more flexibility with formula to apply the same idea to a wider range of circuits, but those days are long gone)
That sounds like a great and fun opportunity - real world testing is certainly different to the college rig!
In the real world I'd be looking at the actual loadings. If I was very worried, I'd probably be looking for a way to get a distribution circuit with very low resistance nearer the bedrooms and supply the bedroom circuits from there.
I doubt this would actually be needed though.
Regulation 433.1.204 seems kind of dumb where it states the 30 / 32 amps on a rfc
dropping the mcb rating does not make it less safe, does it? I mean you can get 25amp mcb now
I feel like it should mean you can use 32 amps on a ring wired in 2.5mm even though the cable is rated lower than 32 amps
So would a ring on 20amps be coded as a c3 or a c2 seems hard to justify if its safe but not a generic circuit design
there is like four sockets per room i think
you would not be concerned with the at 32 amps?
is that because the VD is only a few percent over ? or becasue you doubt they would ever be loaded that much to reach 32 amps?
I don't disagree. Bring back the 14th edition!
My opinion: If otherwise compliant and appearing fit for purpose, C3 if I thought there was no reason it couldn't be 32amp, otherwise I might just put a Note to document that I'd noticed it.
So in this case where it is compliant on a 20 amp, compliant in terms or ZS and VD but not reg 433.1.204 it would be a c3.
Would it be a c3 or c2 if it was on 32 amps complied with ZS but VD was 7.5% in your opinion?
I don't think there's a generic answer. We're not robots! EICRs are a judgement on safety and risk based on experience (I'm very much still learning and will be until I retire). It would depend on how it's being used or is likely to be used, as discussed above.
Ah that Makes sense, I would of thought it would be cut and dry with regards to exceeding VD, that's what im struggling with
....for a RFC is the design current always 32 or (26) or could you have a design current of 25 but still have it on a 32 amp mcb or rcbo?
For clarity, assessing an existing installation is a very different ball game to designing, installing and initial verification of a new installation - in the latter case I would ensure VD rules are met.
Your questions keep flipping between the two scenarios!
Just because you judge something safe on an EICR doesn’t mean you’d copy it!
The other thing - does it seem likely there is 155m of cable from the CU to these bedrooms and back?
What sort of property is this?
Was it a calibrated tester you used?
Being more specific that rule is an exception to the usual case where the protection against overload has to match the cable. In the RFC case you are allowed 50% over due to the two 'legs' of the ring largely sharing the current but they pin it down to this case.
The earlier regs allowed this 50% margin (or the cable CCC is 67% of OCPD) as a general rule, later it became an RFC is 30/32A but I suspect the real reason for changing it was to prevent "creative" designs of a 45A ring on 4mm cable, etc, being created.
No, there is nothing unsafe about a lower MCB and it is something that is not too uncommon as I have seen a couple of RFC that were on 20A rewirable BS3036 fuses. I think in some cases if the supply Ze was originally high then it was to meet ADS times on the fuses.
It seems no real risk of VD being a problem then!
Why?
No, it just makes the ring pointless, it might as well be a radial circuit if you're using a lower rated MCB.
It wouldn't be coded anything as it is not unsafe and there is no safety improvement to be recommended.
No, EICRs are not assessing absolute compliance with BS7671, they are only concerned with safety for continued use. On an EICR this would not be mentioned at all.
Neither, volt drop on final circuits is not something you'd normally consider on an EICR.
It is cut and dry, you design circuits which comply with volt-drop limits to ensure that they function correctly.
On an existing installation you'd only assess volt-drop when planning additions to the installation or when investigating problems in the installation.
A combination of all. Here's how I look at it:
A supply voltage of 216V (lower limit that is permitted to be supplied) supplying a circuit with a 5% voltage drop, gives a voltage of 205.2V at its furthest point when under load - quite low. This is perfectly acceptable according to regulation.
A supply voltage of 245V (common in my experience, much more likely to come across this than 230V) supplying a circuit with a 10% voltage drop gives a voltage of 220.5V at its furthest point under load. Twice the permitted voltage drop as a percentage so non-compliant with regs, yet the working voltage is 15V higher than the previous, compliant example, and is much closer to the 230V the equipment is designed for.
So the working voltage in the 2nd example is 'better' than that in the 1st, despite it being non-compliant.
The downside to the second example is there will be more power wasted as heat through the cables, when under load. For a circuit that is expected to be fully loaded for long periods of time (eg. EV charger), this would be a costly, wasteful problem. However, the average ring final is unlikely to be fully loaded often, if ever. Even if it is, it is unlikely that it will be fully loaded for any length of time, nor is it likely that the bulk of the load will be concentrated at the mid-point of the circuit.
In short, it's unlikely to happen, and if it does, the consequences are likely to be negligible. I'd say the cost of rewiring the circuits will probably outstrip any savings made due to reduced cable losses, many times over throughout the life of the circuit.
London
United Kingdom
Other
If other, please explain
School premisis
Working out the length of a ring finals circuit
Tetris1985,
Pretty Mouth,