r1: 1.15
r2: 1.80
rn: 1.15
r1r2 0.69

To work out the length of a ring in 2.5mm twin would this be correct

0.69/(19.51/1000) = 35m

or would you use the r1r2 before you divide it by 4?
 
Ah that Makes sense, I would of thought it would be cut and dry with regards to exceeding VD, that's what im struggling with

It is cut and dry, you design circuits which comply with volt-drop limits to ensure that they function correctly.

On an existing installation you'd only assess volt-drop when planning additions to the installation or when investigating problems in the installation.
 
you would not be concerned with the at 32 amps?
is that because the VD is only a few percent over ? or becasue you doubt they would ever be loaded that much to reach 32 amps?
A combination of all. Here's how I look at it:

A supply voltage of 216V (lower limit that is permitted to be supplied) supplying a circuit with a 5% voltage drop, gives a voltage of 205.2V at its furthest point when under load - quite low. This is perfectly acceptable according to regulation.

A supply voltage of 245V (common in my experience, much more likely to come across this than 230V) supplying a circuit with a 10% voltage drop gives a voltage of 220.5V at its furthest point under load. Twice the permitted voltage drop as a percentage so non-compliant with regs, yet the working voltage is 15V higher than the previous, compliant example, and is much closer to the 230V the equipment is designed for.

So the working voltage in the 2nd example is 'better' than that in the 1st, despite it being non-compliant.

The downside to the second example is there will be more power wasted as heat through the cables, when under load. For a circuit that is expected to be fully loaded for long periods of time (eg. EV charger), this would be a costly, wasteful problem. However, the average ring final is unlikely to be fully loaded often, if ever. Even if it is, it is unlikely that it will be fully loaded for any length of time, nor is it likely that the bulk of the load will be concentrated at the mid-point of the circuit.

In short, it's unlikely to happen, and if it does, the consequences are likely to be negligible. I'd say the cost of rewiring the circuits will probably outstrip any savings made due to reduced cable losses, many times over throughout the life of the circuit.
 

Reply to Working out the length of a ring finals circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
675
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
298
Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
2
Replies
23
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top