I initially went for answer b) because in GN3 page 68 (2.6.17) I read

"At every relevant point of the installation"

but then I read

The inspector must have knowledge of the design in this report as, for example, if the switchgear at the origin of an installation is suitably rated for prospective fault current and switch gear of similar short circuit rating is used downstream of that point, then no further checks are necessary.

which made me change my mind and go with answer d)

seeing as the correct answer is a) I'm clearly not getting it and wondered if anyone would mind trying to educate me please?
 

Attachments

  • [ElectriciansForums.net] Would anyone mind trying to help me understand this question please
    20210313_123058.jpg
    250.8 KB · Views: 22
I initially went for answer b) because in GN3 page 68 (2.6.17) I read

"At every relevant point of the installation"

but then I read

The inspector must have knowledge of the design in this report as, for example, if the switchgear at the origin of an installation is suitably rated for prospective fault current and switch gear of similar short circuit rating is used downstream of that point, then no further checks are necessary.

which made me change my mind and go with answer d)

seeing as the correct answer is a) I'm clearly not getting it and wondered if anyone would mind trying to educate me please?
DB3 operating at 400v, DB2 operating at 230v. I=V/R. Higher voltage results in higher fault current.
 
DB3 operating at 400v, DB2 operating at 230v. I=V/R. Higher voltage results in higher fault current.

Thanks for trying to help @Lister1987 but I'm not sure if that answers it for me mate.

The questions says

At the origin of DB1, the maximum Ipf was recorded as 8kA

where else must the test be undertaken within the installation.


the options it gives me are

a) DB3 only
b) DB2 and DB3
c) DB2 only
d) Nowhere else

The answer is a) DB3 only

But why is that. Does anyone know
 

Attachments

  • [ElectriciansForums.net] Would anyone mind trying to help me understand this question please
    16157405434051552160921350891786.jpg
    248.7 KB · Views: 14
Thanks for trying to help @Lister1987 but I'm not sure if that answers it for me mate.

The questions says

At the origin of DB1, the maximum Ipf was recorded as 8kA

where else must the test be undertaken within the installation.


the options it gives me are

a) DB3 only
b) DB2 and DB3
c) DB2 only
d) Nowhere else

The answer is a) DB3 only

But why is that. Does anyone know
Due to it being at a different operational voltage, the others are at 230v, so testing then would give identical results to DB1
 
But DB1 is 400v 3 phase DB2 is 230v single these and DB3 is 400v three phase
DB1 has 10kA switchgear, DB3 has 6kA switchgear. You want to test at the lowest rate switchgear to ensure that you measured Ipf (8kA) wil be within its operational limits. Also DB3 (400v) has the higher voltage than DB2 (230v).

In this scenario DB3 would require higher kA rated switchgear to handle the measured Ipf.
 
DB1 has 10kA switchgear, DB3 has 6kA switchgear. You want to test at the lowest rate switchgear to ensure that you measured Ipf (8kA) wil be within its operational limits. Also DB3 (400v) has the higher voltage than DB2 (230v).

In this scenario DB3 would require higher kA rated switchgear to handle the measured Ipf.
Thank you kindly @Lister1987 appreciate you input mate. Nice one
 

Reply to Would anyone mind trying to help me understand this question please in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top