hi all have been doing some pir,s recently an im a little rusty on a few things got lots more to do an experience is key got a query re a small domestic house with a main board being fitted with rcd as a main sw, protecting approx 4 ccts, lts/ skts/cooker/ shower... on the lts cct also has the alarm and smokie with no seperate fused connection unit
would i recommend the following,
1. no additional protection
2. incorrect main sw
3. circuits not seperated


any help with this and any help with the inspection checklist would be great
 
if the board was fitted prior to 17th, then the above points are IMO just a code 4. with the xception of the alarm. it should have it's own FCU or it,s own MCB. the smokes are fine if wired into a frequently used lighting circuit.
 
hi all have been doing some pir,s recently an im a little rusty on a few things got lots more to do an experience is key got a query re a small domestic house with a main board being fitted with rcd as a main sw, protecting approx 4 ccts, lts/ skts/cooker/ shower... on the lts cct also has the alarm and smokie with no seperate fused connection unit
would i recommend the following,

1. no additional protection If the main switch is an RCD then ALL circuits have additional protection (assuming it's 30mA).

2. incorrect main sw Can you back up your thoughts on why you think it is incorrect though??? for me it would warrant a code 4 in this instance.

3. circuits not seperated Well they are, as you have 4 circuits and it is quite common for smoke alarms to be connected to lighting circuits.


any help with this and any help with the inspection checklist would be great

The other alarm to which you refer is that a security alarm with no means of isolation other than the lighting MCB???

What area's are you not understanding about the inspection schedule???
 
Last edited by a moderator:

Reply to would like advice on main board with rcd being used as main sw in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
725
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top