Looks to me like an 11kV Ring Main Unit (one half of) with the sides cut away or a MV switch with integral earthing. Oil filled given the look of the internals and it could be anywhere from 40 years + to more recent. If its a switch then the description below applies, if its a RMU picture two switches with a common point in the middle.
The center part is where an incoming / outgoing feed would be attached, the left hand part the outgoing user. Typically fused or oil filled circuit breaker to a transformer in the MV distribution. Operation is generally manual in this type of switchgear (ie by someone operating a handle external to it).
Picture the centre part swinging clockwise, that would make the circuit. The extended slim piece of copper is used to allow the main conducting faces to break before (or make after) the roller part will so preventing them from suffering any arc damage from breaking the circuit. It also increases the arc path on opening making it easier for the oil to quench it.
If the operation was anti-clockwise from that shown, then that puts the feed attached to an earth position. The position shown is the isolated position.
Still in common use all over the country due to their rugged design, low maintenance requirements and their cost factor - very low compared to SF6 or vacuum equivalents. Also the fact that they are manual operated and do not require any power supplies etc.
The bottom 3 transformers are each fed by a RMU with a circuit breaker providing isolation and protection for them. Whats not shown below is the earthing position of the breaker, but you can see that each RMU has an incoming switch, an outgoing switch and an outgoing feed to the transformer.
Incidentally, it is the type of switchgear referenced in
this post
ps. I couldnt find a decent schematic or cutaway of one of them to attach.