This is my first post so please be gentle!
I've been asked to extend an RFC into an extension at the back of an 8 year old property.
It is a TN-C-S supply with 2 RFC's, one for the Kitchen and one for the rest of the house.
I've done some testing on the main house RFC as follows:
r1=0.84
rn=0.84
r2=1.53
R1+R2 = 0.59
Zs= 0.78
All figures are pretty close to their theoretical values so happy so far.
My issue is when calculate the length of cable I come out with 0.84/0.00741 = 113 metres
According to table 7.1(i) in the onsite guide the maximum length of cable for a standard circuit of 2.5/1.5 protected by type B MCB is 106 metres so this circuit is already outside of the limit.
I have the current volt drop calculation as Vd = L x Ib x (mV/A/M)/ 4 x 1000.
So VD = 113 x 32 x 18 /4000 = 16v
5% of 230V = 11.5, so its already over the allowable 5%
This is very disappointing as this is a relatively new build and there are spares in the board. I am surprised that the designer did not install two separate RFC's, one for up and one for down.
The extension is relatively small, 4m x 4m so extending the ring will add a maximum of 16 metres which would cost the customer very little.
The alternative is a new radial circuit from the CU at the front of the property and on the opposite side of the house which means all floor boards up and a very costly job.
There are no fixed loads on the ring and just the usual T.V's, games consoles lamps etc so loading is not an issue and I cant see volt drop being a problem and Zs is good.
What would you do? I think I've answered my own question with my calculations!
Thanks for your help.
I've been asked to extend an RFC into an extension at the back of an 8 year old property.
It is a TN-C-S supply with 2 RFC's, one for the Kitchen and one for the rest of the house.
I've done some testing on the main house RFC as follows:
r1=0.84
rn=0.84
r2=1.53
R1+R2 = 0.59
Zs= 0.78
All figures are pretty close to their theoretical values so happy so far.
My issue is when calculate the length of cable I come out with 0.84/0.00741 = 113 metres
According to table 7.1(i) in the onsite guide the maximum length of cable for a standard circuit of 2.5/1.5 protected by type B MCB is 106 metres so this circuit is already outside of the limit.
I have the current volt drop calculation as Vd = L x Ib x (mV/A/M)/ 4 x 1000.
So VD = 113 x 32 x 18 /4000 = 16v
5% of 230V = 11.5, so its already over the allowable 5%
This is very disappointing as this is a relatively new build and there are spares in the board. I am surprised that the designer did not install two separate RFC's, one for up and one for down.
The extension is relatively small, 4m x 4m so extending the ring will add a maximum of 16 metres which would cost the customer very little.
The alternative is a new radial circuit from the CU at the front of the property and on the opposite side of the house which means all floor boards up and a very costly job.
There are no fixed loads on the ring and just the usual T.V's, games consoles lamps etc so loading is not an issue and I cant see volt drop being a problem and Zs is good.
What would you do? I think I've answered my own question with my calculations!
Thanks for your help.