[ElectriciansForums.net] Wylex 3 phase board fitting.

Do I need any more than this to fit the above board, does it need a fitting kit for the switch or anything extra to get it up and running (tails excluded obviously)
 
You have to remember that the SPD is trying to divert the surge current. So if the supply goes above 500V-ish it starts to conduct rapidly and in order to dump a few kA of surge, and at for no more than a kV or so of let-through voltage, it has to have a dynamic impedance (dV/dI) of under an ohm.

But that all happens very quickly (tens of microseconds), so if the SPD's cable has any significant inductance that make the SPD look like a higher impedance, so you get less current diverted and so a bigger voltage let-through.

The SPD and its cable is a shunt across the supply, so the length of supply cable feeding it is not important, it is the length of cable between the supply L/N/E and the SPD terminals that determines how well it is able to shunt that current away (heating up internally in the process).
That makes sense thanks, must have been what JW was getting at ut I couldn't remember it.
 
Here is an attempt to make the SPD wiring effect more obvious:
[ElectriciansForums.net] Wylex 3 phase board fitting.
The surge on the supply is usually limited on LV networks to around 6kV open-circuit as above that something upstream will tend to flash over. While the supply cable impedance tends to 50-80 ohms for long lengths (its characteristic impedance), for 100kHz that is longer than 2km so not likely, and for shorter cables (i.e. surge closer to the SPD) it looks close to some R & L and often is as low as an ohm or so, so the surge current is often taken as around the 3kA or so region.

So your typical surge might be of the order of 3kA and 1.5kV over the SPD which is about 4.5 MW. While that is a lot of power, it is typically only for around 20us or so, so represents about 90 J of energy/heat.

Looking up zinc oxide as the typical material for a MOV surge protective device, if we take it as weight about the same as a 20p coin = 8g then it is about 0.1 mole of compound. The heat capacity is given as 40.3 J/K/mol so such a 90J surge will heat the disk up by about 23 K which is easy to survive.

Doing the same for the ~350us surge from a direct hit on to some aspect of the power system (or local ground linked to a lightning conductor), instead of the ~20us from a nearby strike inducing current, you have a disk temperature of hitting about 410 C and so melting the contacts for safe disconnecting. Next hit and your electronics is toast...

The bigger type 1(+2) SPD often use GDT (gas discharge tube) so when they fire the volts drop down to ~100V to keep the device's dissipation down by a factor of 10-15 compared to a MOV that tries to tough it out, but they have issues of mains AC current follow-through so sometimes have a lower voltage MOV in series to try and let any arc quench on the AC zero-crossing much faster, etc.

But looking at the lower circuit you can see that the L of the SPD's cables is in series with the surge current, so the volt drop along their inductance is presented to the load. Which it might not enjoy.
 
Thanks for the explanation, I'm not sure I understand everything but sort of get it, I've watched big clive tear down SPD devices before now and ween the gas discharge tubes inside them. I think the simplest explanation is it matters how short the cables are when they are across the mains as opposed to in-line with them.
 
Got loads of Wylex metal blanks, I presume they will fit in. As for surge, I'm going to fit a 3rd party one in an external enclosure, the price of the wylex one is ridiculous. Thats if it needs a SPD at all, not too sure of the commercial regulations.
I have not come across many scenarios when i can omit surge protection . If Anything is going to be more expensive to repaire that the cost of the surge unit. Then I fit one. For example high level light would expensive to repaire if scissor lift was required.
 
Got loads of Wylex metal blanks, I presume they will fit in. As for surge, I'm going to fit a 3rd party one in an external enclosure, the price of the wylex one is ridiculous. Thats if it needs a SPD at all, not too sure of the commercial regulations.
Never use metal blanks on a vertical mounted installation as I learned the hard way few months back doing a strip out on a old bupa building everything labeled up incorrectly (as I know know )removing the db cover to cheak it was isolated and one of them metal blanks slid down and landed directly across two phases sore eyes and alot of metal splash
 
The boards I ended up getting came with a load of plastic clip in blanks, very flimsy and wouldn't take very much to push through but obviously wylex thinks they are good enough and they must be compliant otherwise they wouldn't include them.

As for the metal blanks, the ones that you have to put in at an angle that slide about all over the place are the worst blanks I've ever tried to fit, however Wylex have come up with a new design of metal blank that clip in like the older plastic blanks did and you can fit them after the lid is on, they grip the lid really tightly as well so no chance of them falling out or sliding about.
 
As for the metal blanks, the ones that you have to put in at an angle that slide about all over the place are the worst blanks I've ever tried to fit, however Wylex have come up with a new design of metal blank that clip in like the older plastic blanks did and you can fit them after the lid is on, they grip the lid really tightly as well so no chance of them falling out or sliding about.
They are an improvement for sure, a bit like the Axiom ones oddly enough.
 

Reply to Wylex 3 phase board fitting. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
645
What makes it a lack of space? I’d say to the customer to dismantle a cupboard or whatever to creat the space you need for the extra equipment...
Replies
1
Views
228

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top