Hi Peeps,
Doing an EICR where a shower cable is 6mm[SUP]2 [/SUP]from the CU to the pull switch then 10mm[SUP]2[/SUP] to the shower. Assuming the 6mm cable is rated at 47A then the Wylex 50A MCB fails In<Iz.
It's a 9.5kW Shower so is pulling 41A therefore a 45A MCB would be perfect to meet the demand whilst being rated less than the cable. The only problem is Wylex don't make a 45A MCB so who else makes one that will fit?
I'm not totally happy with putting in a 40A one as overheating alarm bells are ringing in my head. I don't fancy rewiring 10mm between the CU and the switch either.
Thanks in advance. Oh and ignore the Trainee status I don't know how to change it.